Jump to content
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 27 April 2024 02:00 PM Until 03:00 PM
      5  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological. 
      We have a special session planned for this one. Instead of the usual Show 'n Tell on a technical topic, we're going to post tech sheets in the comments to this Calendar Event (scroll down to see what's posted so far) and ask specific questions that can only be answered by reading the tech sheet. If you at least try to answer the questions beforehand, you'll get a lot more out of it. The tech sheet and the questions are posted in the comments section below.
      Your mission, if you should choose to accept it, is to check out the questions for each one and try to answer them ahead of time. Then come to the Dojo to see how well you did! 
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, April 27 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Blower Speeds


Jason

Recommended Posts

Hello, new to the forum, thanks for having me. My question is now that i turned my furnace on for the year the blower seems to be slower for some reason, when i place my hand over the floor register it has little volume of heated air coming out, the blower is running but i don't think fast enough. Any ideas it is a lennox diplomat.

Thanks in advance...

Link to comment
Share on other sites

  • Replies 1
  • Created
  • Last Reply

Unless your hand is calibrated to "feel" cfm(cubit feet per minute) I would suggest a simple temperature rise check at the furnace.

Measure the air temperature at the return air duct (should be about room temp) then measure the supply air temperature a few feet downstream of the plenum. Subtract the return air temp from the supply air temp and compare this to the rating on the name plate (ie - 40-70F). If the temperature rise is above the rating then speeding up the blower is an option after you verify the filter is clean, the blower wheel is clean, the a-coil is not plugged, and all registers and return air grilles are open.

Link to comment