Jump to content
LIMITED TIME OFFER: Use code 10YEARS10 to get 10% off your Appliantology membership. Click here for more ×
Click here to check out our structured, online appliance repair training courses for rookies and experienced techs.

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 27 April 2024 02:00 PM Until 03:00 PM
      0  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This workshop is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      If you have a specific appliance problem you'd like us to talk about, post it here! We need a problem statement and a PDF of the tech sheet or schematic so we can all see it on screen share. If you have a PDF that isn't already in the File library here at Appliantology, send it to us by attaching it to the contact form. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, April 27 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Carrier 58MXA080-8-1-20 inadequate return air supply


owlfan12000

Recommended Posts

I had this unit installed about 4 years ago. It went out last night and the technician found a crack in the pressure switch hose end. It was quickly repaired. Then the technician noted that the unit was giving a trouble code of 31. He determined that the return air duct was inadequate for the furnace size. The unit has apparently been short cycling for the past four years.

He then tried to tell me that it really didn't hurt the unit and probably only cost me an extra dollar or two per month in energy costs. For the record the technician was from the company that sold and installed the furnace.

I'm an Electrical Engineer so I'm not buying that but I have no HVAC experience and I'm not well equipped to argue the point. It seems to me that an inadequate air supply will, at the very least mean that the natural gas combustion would not be complete and more natural gas would be required to provide the same heat to the house.

Can you give me any details on the possible ramifications of this problems? If memory serves I think this unit also provides forced air for my central air unit. Could this have impacted my AC cost as well as my heating costs?

Link to comment
Share on other sites

  • Replies 1
  • Created
  • Last Reply

58MXA080-8-1-20

Fault code 31 indicates "pressure switch failed to close" which is exactly what it should be given the pressure switch hose was cracked (not typical by the way on a 4 year old furnace) -

As for inadequate return air, it has absolutely nothing to do with the combustion process. Combustion air is brought in through the pvc pipe into a sealed combustion chamber then exhausted through another pvc pipe.

However inadequate return air will cause a furnace to cycle on the hi limit control(causes stress on the heat exchanger). Your furnace is rated for 40-70F temperature rise, meaning if the return(room air) temp is 70F then the supply air can be as high as 140F (recommended rise is 55F). Take a temperature measurement a few feet downstream from the supply pleneum and subtract the room air temp. Allow the furnace to come up to temp for 5 minutes or so before taking the reading.

On new equipment start-up this would have been a required set-up check. Keep us posted...