Jump to content
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 30 March 2024 02:00 PM Until 03:00 PM
      0  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This workshop is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      If you have a specific appliance problem you'd like us to talk about, post it here! We need a problem statement and a PDF of the tech sheet or schematic so we can all see it on screen share. If you have a PDF that isn't already in the File library here at Appliantology, send it to us by attaching it to the contact form. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, March 30 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

SQ D Contactor failure


edwardh1

Recommended Posts

This square D 40 amp (200 amp LRA rated) contactor , mexican made in a 30 running amp amp air conditioner load failed after 2 years.

The service company put in a Siemens to replace it, said SQ D were "cheap" . The heating started in the lower right and the plactic bulged out and melted on the right side. Anyone else had similar problems?

post-27-12904509402_thumb.jpg

Link to comment
Share on other sites

  • Replies 5
  • Created
  • Last Reply

I go through at least 20 contactors a season and I don't even do a lot of HVAC. It's clearly a part designed to make work for us.

Link to comment
Share on other sites

  • 1 month later...

  Basically there are 2 standards of contactors / starters:

 NEMA ( National Electrical Manufacturers  Association ), and IEC ( Intertechnical European Commision ), or something like that. The NEMA standard is generally heavier duty than the IEC. They are rated for more cycles off / on, and the contacts are also heavier. The advantage of the IEC, is size. If you are in a tight spot, then this may suit you better. I have used them on several occasions, but generally dont max them out, on the FLA ( Full Load Amps ). Go to the next bigger size, just to be on the safe side. I would think the Square D would be NEMA.....but then again, maybe not. I know Cutler Hammer has both to choose from, so possibly Square D has both as well. It should say on the contactor whether it is NEMA or IEC rated.

Link to comment
Share on other sites

obviously the heat damage is the visual evidence of current draw.

How old is your machine (perhaps the compressor and or outdoor fan motor is having a harder time starting up due to wear and tear or capacitors outside of spec).

Since it is a heat pump, are the coils clean (dirty coils causing higher pressures in the cooling mode causing a greater load on  the compressor).

What is the mega ohm reading on your windings (are the windings breaking down causing minor winding to winding shorts or excessive heating in the windings).

What is the wire gauge serving the disconnect and the contactor and what is the length (would not be the first time that too small a gauge was used - especially on a previous change out).

Check and make sure that the disconnect is fused withing the OEM max rating (I find disconnects with fuses that are in excess of OEM specs all of the time.  This will allow the unit to draw too much current and not blow thereby hiding a true problem that needs attention but shows up as a symptom elsewhere in the system).

Just some things to consider in an effort to get you an answer other than "It is a cheap piece of crap contactor."  Look hard enough and you will most likely find your answer

Link to comment
Share on other sites