Jump to content
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 27 April 2024 02:00 PM Until 03:00 PM
      0  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This workshop is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      If you have a specific appliance problem you'd like us to talk about, post it here! We need a problem statement and a PDF of the tech sheet or schematic so we can all see it on screen share. If you have a PDF that isn't already in the File library here at Appliantology, send it to us by attaching it to the contact form. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, April 27 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Troubleshooting Industrial Trane Chiller


winenotwhine

Recommended Posts

winenotwhine

What does error message "Low Press Control Open--Circ one" means. I maintain a winery--before I call out a Trane Tech for mucho dollars,  can anyone tell me what might be going on here?

Link to comment
Share on other sites

  • Replies 2
  • Created
  • Last Reply

Low Pressure Circuit Open means that the temp/pressure of the refrigerant in the system is below a certain cut out level.  Here a few possibilities:

Lack of refrigerant

Light load on the system (not much heat to be moved out of the controlled space)

Liquid line drier may be clogged - restricting refrigerant

Expansion valve powerhead may have lost its charge

Obstruction before expansion valve (filter drier, foreign debris, crimped line)

Low water flow (clogged strainers, defective water pump/impeller)

Some of this you can nose around and check for yourself, some of it you will definitely need to call out a Tech (Trane or otherwise).  The Trane Boys do good work; however, they are not the only ones who know how to work on that kind of equipment.  Shop around.

Link to comment
Share on other sites

winenotwhine

Thanks. It's likely light load. With mild spring time temps I'm only cooling one 75' x 30' room with 16' walls and R30 insulation.

Link to comment