Jump to content
Click here to check out our structured, online appliance repair training courses for rookies and experienced techs.

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 27 April 2024 02:00 PM Until 03:00 PM
      5  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological. 
      We have a special session planned for this one. Instead of the usual Show 'n Tell on a technical topic, we're going to post tech sheets in the comments to this Calendar Event (scroll down to see what's posted so far) and ask specific questions that can only be answered by reading the tech sheet. If you at least try to answer the questions beforehand, you'll get a lot more out of it. The tech sheet and the questions are posted in the comments section below.
      Your mission, if you should choose to accept it, is to check out the questions for each one and try to answer them ahead of time. Then come to the Dojo to see how well you did! 
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, April 27 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Wiring short in Goodman CPE42-1fb condensing unit


fstapanowich

Recommended Posts

We noticed our heat pump putting out cooler air than normal & running for a long time the past few days. Then discovered the fan blades on the condensing unit where not spinning. I went out & tapped the unit & wiggled the 220 wire and saw sparks. Immediatly killed the power to the unit for the night.

Next day I took the cover off & found 3 wires shorted out between the contactor/coil & defrost control board. The 220 supply wire (lower left screw), the white wire (c contact), and yellow wire (y contact). They were fused together. Also noticed the 220 ground wire was loose.

Replacing the wires is simple. My questions are:

1. While the contactor/coil is slightly burned it looks in good shape. Is there a way to test it? Can I just clean it up & continue to use it. Online pricing seems to be around $50. High enough to not want to replace it but happy to do so if it could be a future problem. Hopefully my local supplier has one in stock.

2. Anything else I should check? Is this type of short common for these units?

3. Also, was suprised to find animal droppings inside the unit..but no animals. Is this common? I asume it's warm in there.

Thanks for any suggestions

Link to comment
Share on other sites

  • 3 weeks later...
  • Replies 1
  • Created
  • Last Reply

Kill all the power going into the unit at the pullout.

Check the coil for continuity

 Manually press down on the contactor.Check for continuity between each pole. make sure you take one side of each pole loose so you do not get a false reading from a coninuous loop. Pictured below is a 2 pole contactor.

post-4554-129045098993_thumb.jpg

post-4554-129045099211_thumb.jpg