Jump to content
Click here to check out our on-demand appliance repair training webinars.

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 30 March 2024 02:00 PM Until 03:00 PM
      0  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This workshop is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      If you have a specific appliance problem you'd like us to talk about, post it here! We need a problem statement and a PDF of the tech sheet or schematic so we can all see it on screen share. If you have a PDF that isn't already in the File library here at Appliantology, send it to us by attaching it to the contact form. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, March 30 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Frigidaire FAA055P7A Window Air Conditioner does not cool


FritzS

Recommended Posts

Our Frigidaire FAA055P7A 5200 BTU Window Air Conditioner stopped cooling after 13 months - it worked fine during the warranty period...

The fan operates fine and I am fairly sure that I hear the compressor turn on and off with temp setting changes, but there is no cool air and the coils never become cool to the touch.  I followed the steps in the "Avoid Service Checklist" in the manual, but no change.

Any thoughts on a possible fix?  I might be willing to open the unit up, but the cost/time of repair might push me toward a new unit ($160).

Thanks for any help.

- Fritz

Link to comment
Share on other sites

  • Replies 4
  • Created
  • Last Reply

Sounds like either the  compressor has broken internally or you have lost your freon, if these are not in warranty it would cost less to replace the unit, see what the warranty on the sealed system is in your users manual..

Link to comment
Share on other sites

  • 2 weeks later...
  • 1 month later...

Check your coils!

Do they need cleaned.

A dirty condenser [the one that gets hot] will tell on itself by freezing the evap coil [cold one].

A dirty evap coil will likewise freeze with no airflow. [clogged coils/filter]

Ice is an insulator and will not allow the unit to cool.

Low refrigerant is the last thing to check!

Is the compressor sweating?

Always start with the most obvious before opening a system [tapping line for pressure checking] and introducing noncondensables [ie..air, moisture ect..] into a sealed unit

Good luck!