Jump to content
Click here to check out our on-demand appliance repair training webinars.

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 30 March 2024 02:00 PM Until 03:00 PM
      0  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This workshop is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      If you have a specific appliance problem you'd like us to talk about, post it here! We need a problem statement and a PDF of the tech sheet or schematic so we can all see it on screen share. If you have a PDF that isn't already in the File library here at Appliantology, send it to us by attaching it to the contact form. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, March 30 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Ruud Gas Powervent 2 Water Heater


mac42718

Recommended Posts

I noticed that the gas valve indicator light was blinking four times which according to the troubleshooting manual means that the pressure switch is open. I removed the fan assembly from atop the heater and noticed that there was quite a bit of water in the fan housing. I poured the water out of the fan housing and estimated it to be at least a cup of water that had collected in there. I put everything back together and sure enough the gas burner and all fired back up with no problems. Five days later, the same issue happening again with more water collecting in the fan housing. Why is so much condensation collecting in the fan housing?

Link to comment
Share on other sites

  • Replies 1
  • Created
  • Last Reply

from Power Vent 2 Water Heaters Use & Care Manual

Draining the Condensate

In certain conditions, installations in unconditioned space or

having long horizontal or vertical runs may accumulate condensate.

In order to prevent condensate from draining back into the blower,

we recommend a condensate tee and drain to be installed in a

horizontal vent section as close as practical to the blower vent connection.