Bard Wall Mounted A/C Model WA372-A10 Package EHWA03-A10


  • Please log in to reply
5 replies to this topic

#1 papollonia

papollonia

    Yamabushi

  • Grasshoppah
  • PipPip
  • 94 posts

Posted 21 June 2010 - 07:13 AM

Hey Guys:

I work at my kids school as General Maintenance.

We have 5 modular building.

Each has about 10 Bard Wall Mounted A/C Model WA372-A10 Package EHWA03-A10 Units.

I am stumped on this one!!

One of the Modular building, the A/C was working on Friday when i left.
I come in today and none of them are working.

Checked the Following:

The power switch on each unit (was on)
Checked the circuit breaker (flipped it back and forth) it is 'On'
Check T-Stat - Set to 75degree, temp in rooms about 88 degree.
T-Stat is set to a/c.

ANy Ideas here?

I have a feeling i am missing something that is right in front of my face!!

Thanks


Use the Appliantology Parts Search Box to Find What You Need!
Enter your model number, part number, type of appliance, brand, or even a part description.
365-day return policy on all parts purchased here, even electrical parts that have been installed!

#2 RegUS_PatOff

RegUS_PatOff

    Sensei

  • Academy Instructor
  • PipPipPipPipPip
  • 33,588 posts
  • Location: USA
  • Flavorite Brew:Chief NTSC Black & White

Posted 21 June 2010 - 07:27 AM

[user=42812]papollonia[/user] wrote:

... I have a feeling i am missing something that is right in front of my face!!

Is there some type of "Timer" that shuts off the Systems at the end of the school year ?
.

one of my video productions: “Easter Seals: Walk With Me”

every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962

RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw

#3 papollonia

papollonia

    Yamabushi

  • Grasshoppah
  • PipPip
  • 94 posts

Posted 21 June 2010 - 08:43 AM

Thank you for replying.

 
Not that I know of.


#4 dkpd1581

dkpd1581

    Sōhei

  • Sublime Master of Appliantology
  • PipPipPip
  • 199 posts

Posted 28 August 2010 - 05:42 PM

Verify 208/230 VAC to transformer. 

Verify transformer is tapped for correct incoming voltage.  Transformers set at 230 VAC tap but being supplied with only 208 VAC will not produce a LV signal of at least 22 VAC to run LV system.  Retap as necessary.

Check to see if there is 24 VAC coming out of the transformer - if not find reason why the high side windings are open or 3-5 amp fuse is blown.

If 24 VAC is coming out of the transformer and through the 3-5 amp circuit, follow it through the LV circuits - going into board and not out is possible bad board.  Out of board but not to contactor -  possible limit switch open (HP manual reset, LP auto reset defective).

No board - follow through relay coils - coils open replace relay.  Coils good but contacts do not change state - replace relay.

24 VAC to contactor coil of compressor and/or fan contactor relay but no change of state in contacts same as above.  If contacts change state but full voltage registered across closed contacts means the contact surface is bad or obstructed.  Clean contacts or replace as necessary.

24 VAC circuit is closed and completing a proper path, contactors change state, and zero voltage is registered across closed contacts, check OL switch on compressor, check physical connections in HV circuit, compressor windings for shorts to ground, partially shorted windings, open windings.

If compressor tries to start but is unable to, pulls locked rotor amps and quits, check the capacitor and verify that its within 10 percent of name plate value - if not replace.  If all else is good install a hard start capacitor.

If compressor tries and fails to start with all the above, you may have a physically locked up compressor and a last effort is to strike the compressor head on start up in an attempt to dislodge the seizure.

Try this and let us know what happens.





#5 AmTec Services

AmTec Services

    Sōhei

  • Chief Appliantologist
  • PipPipPip
  • 158 posts

Posted 31 August 2010 - 03:55 PM

If all are not working (5?) it seems you need to look for a common link. Timers,energy managment devices, or fire alarm circuits are all suspect when you have multi nothing runs problem. Look for the common link.

........................AmTec

The futures so bright, I gotta wear shades!

#6 Dan Webster

Dan Webster

    Paw Paw

  • Academy Fellow
  • PipPipPipPipPip
  • 1,320 posts
  • Location: USA
  • Flavorite Brew:Busch

Posted 01 September 2010 - 08:23 AM

All 5 units are out at once? Sabotage!

"May the hinges of our friendship never grow rusty"
-old Irish saying

Buy me a Beer: http://web.me.com/ze...man18007260692/





0 user(s) are reading this topic

0 members, 0 guests, 0 anonymous users


FAQs | Store | Memberships | Repair Videos | Newsletter | Beer Fund | Contact


Use the Appliantology Parts Finder to Get What You Need!
Enter a model number, part number, type of appliance, brand, or even a part description.
365-day return policy on all parts purchased here, even electrical parts that have been installed!

Your Sometimes-Lucid Host:
Samurai Appliance Repair Man
"If I can't help you fix your appliance and make you 100% satisfied, I will come to your home and slice open my belly,
spilling my steaming entrails onto your floor."

The Appliance Guru | AppliancePartsResource.com | Samurai's Blog

Real Time Analytics