Jump to content
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 27 April 2024 02:00 PM Until 03:00 PM
      5  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological. 
      We have a special session planned for this one. Instead of the usual Show 'n Tell on a technical topic, we're going to post tech sheets in the comments to this Calendar Event (scroll down to see what's posted so far) and ask specific questions that can only be answered by reading the tech sheet. If you at least try to answer the questions beforehand, you'll get a lot more out of it. The tech sheet and the questions are posted in the comments section below.
      Your mission, if you should choose to accept it, is to check out the questions for each one and try to answer them ahead of time. Then come to the Dojo to see how well you did! 
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, April 27 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

COLEMAN/EVCON DGAT070BDC HEATING AND AIR SYSTEM


ANGELIZBETH

Recommended Posts

ANGELIZBETH

I HAVE A COLEMAN/EVCON HEATING AND AIR SYSTEM AND THE NIGHT BEFORE LAST IT JUST QUIT NOW THE OUTSIDE UNIT WORKS GREAT BUT THE INSIDE PART DOES NOT IT ACTS LIKE IT IS NOT GETTING ANY ELECTRICITY TO IT BUT I KNOW IT IS BECAUSE WHEN I WIGGLED THE WIRES I GOT A LITTLE SHOCK THERE ARE NO LIGHTS ON, ON IT ANYWHERE COULD IT BE MOTOR OR THERMOSPLEASE HELP THE MODEL NUMBER IS DGAT070BDC

Link to comment
Share on other sites

  • Replies 2
  • Created
  • Last Reply

Well your transformer is fine because you can get the outside to come on. Is yours a gas furnace? If it is then look for a fan relay on the beast. Why do we need a fan relay? Well on gas heat the fan must blow at a much slower speed than cooling mode which needs to be on high speed. So when you call for cooling the outside unit comes on and the relay gets energized to shift the fan from low for heat to high for cooling. The fan relays on most American units look a lot like THIS. On the wall themostat is a lever that has "AUTO" and "ON" shift the lever to "ON" and if that relay is bad the fan oughta come on. If it still don't come on check it to see if it may need oiling. Use zoomspout oil on that motor. DO NOT USE WD-40 (flammable oil and old linty motors don't work too good). Look at the capacitor on the fan motor. It could be bad. After it is energized it oughta spark monetarily when shorted, no spark no good. Take the capacitor to the HVAC store. they will check it for you.

Link to comment
Share on other sites

COLEMAN EVCON RESIDENTIAL FURNACE CONTROL BOARD

Note: There has been changes to this board on many of the Coleman Furnaces. This kit may require the services of an HVAC Company to install depending on your qualifications.

As you can see, some furnaces will need the wiring harness changed with the supplied harnesses and instructions. The board you have MAY not look like the one below and that is why you may need to change these wires! You may not need all the wires supplied, follow the instructions that come with the kit!

post-30745-0-93231200-1308782425_thumb.j