Payne 394 upflow furnace
#1
Posted 28 July 2011 - 05:08 PM
#2
Posted 28 July 2011 - 05:20 PM
The relay might be clicking but not making contacts inside. A furnace uses low speed to operate the heat and is always wired to run on low. When air condition is called for the relay clicks and switches from low speed to high speed for cooling. Might be the contacts in there are fried.
Post some photos of your blower and the controls for a more precise answer. Let us see what you have if you can.
Attached Files
"May the hinges of our friendship never grow rusty"
-old Irish saying
Buy me a Beer: http://web.me.com/ze...man18007260692/
#3
Posted 28 July 2011 - 05:31 PM
The motor spins freely and wht I think is the capacitor looks really ugly unit is about 20 yrs old and 2 years ago I replaced the circuit board as soon as the wife gets home I will post some photos
Edited by ridodami4, 28 July 2011 - 05:33 PM.
#4
Posted 28 July 2011 - 05:54 PM

#5
Posted 28 July 2011 - 07:11 PM
Capacitor may look like this :
one of my video productions: “Easter Seals: Walk With Me”
every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962
RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw
#6
Posted 29 July 2011 - 07:04 AM
turn off power to unit
At the circiut board find and remove the PR-1 wire. move it out the way.
Find the black wire marked HI on the board . remove HI wire and place on PR-1 terminal.
You are now directly powering the fan motor(bypassing the circuit board) to test the motor .
Put cover back on blower and turn on power to heater. The motor will run now if it is ok.
If the motor runs replace the circuit board.
If the motor does not run replace the motor and capacitor.
Edited by ACtechGUY, 29 July 2011 - 07:48 AM.
#7
Posted 29 July 2011 - 10:31 AM
#8
Posted 29 July 2011 - 02:54 PM
It is often the case when a motor is failing it will draw alot more amperage than the relay contacts are rated for and burn out the board.
It is very possible to have a failed / failing motor and a burnt control board.
#9
Posted 02 August 2011 - 08:29 PM
Total cost $198.99. thank you all for your responses, Ridodami4
And the beer of the day for today is...Flying Dog Double Pale Ale!!
0 user(s) are reading this topic
0 members, 0 guests, 0 anonymous users
FAQs | Parts | Memberships | Repair Videos | Newsletter | Beer Fund | Contact
Your Sometimes-Lucid Host:
"If I can't help you fix your appliance and make you 100% satisfied, I will come to your home and slice open my belly,
spilling my steaming entrails onto your floor."
ApplianceGuru.com | AppliancePartsResource.com | Fixitnow.com