Trane XR80 gas furnace blower motor loud buzzing
#1
Posted 01 August 2011 - 01:18 PM
#2
Posted 01 August 2011 - 02:01 PM
could be ..... Do you think the run capacitor is the culprit?
you can test the Capacitor (somewhat) with an OHM meter
After discharging the Capacitor, use your OHM meter on the 20 Meg scale...
should start with a low reading and slowly rise.
Reverse the leads and try again ..
(may start with a "negative" OHMs and rise to 0 and then infinity)
one of my video productions: “Easter Seals: Walk With Me”
every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962
RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw
#3
Posted 01 August 2011 - 02:13 PM
#4
Posted 01 August 2011 - 03:17 PM
Edited by applianceman18007260692, 01 August 2011 - 03:19 PM.
"May the hinges of our friendship never grow rusty"
-old Irish saying
Buy me a Beer: http://web.me.com/ze...man18007260692/
#5
Posted 01 August 2011 - 03:20 PM
... not necessarily...... It should make a small pop if it is holding a charge. No pop no good.
It's an AC Cap, if the unit was turned OFF at or near the "0 crossing" of the AC Sine Wave, it won't "pop"
one of my video productions: “Easter Seals: Walk With Me”
every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962
RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw
#6
Posted 01 August 2011 - 04:37 PM
Run Capacitors discharge via the motor. When a "good" capacitor is in the circuit with a "good" motor the capacitor will discharge any voltage Very rapidly (as in seconds or less).
If you can get a capacitor to "pop" . you likley have a failed motor or broken wire in the motor circuit.
YOU SHOULD NEVER SHORT THE TERMINALS OF A CAPACITOR . You may DAMAGE a capacitor by dead shorting the terminals or it may decide to explode in your face.
If you are unsure if your capacitor is holding a charge, Use Your voltmeter set to the AC volts setting . Put your leads on the terminals. the capacitor will discharge thru your meter . and because you have a meter that is designed to not be a dead short , you do not damage the capacitor.
Edited by ACtechGUY, 01 August 2011 - 05:50 PM.
#7
Posted 01 August 2011 - 05:28 PM
At 10 years old I would think a failed motor is very possible. 10 yrs is the standard lifespan of a motor these days( sometimes only 5 years!!)
A failed (electrically ) motor will spin just fine by hand .
You can Check for a failed motor by taking an OHM reading with your digital volt meter.
On a 1/2 hp 115volt blower motor here are the readings you should generally see:
Between White(common wire) and Black (high)- 6 ohms
Between White and blue (medium) - 9 ohms
Between White and red (Low) - 15 ohms
Between white and brown with white stripe(capacitor) - 0 ohms or very little
Between White and brown ( capacitor) - 45 ohms
Resistances will vary from motor to motor.
Also your motor may be a different horsepower along with the very distinct possibility that it may also have more speeds than I have shown .
If your motor differs from the one i show the resistances would be not be the same ,but as you can see , there is an increase in resistance as you go from the highest speed to the lowest speed. One of the Brown wires will always have little to no resistance and the other brown wire will have the highest resistance of all.
This will apply to all motors.
If your motor does not conform to this , it is BAD.
Edited by ACtechGUY, 01 August 2011 - 05:42 PM.
#8
Posted 01 August 2011 - 08:04 PM
On a 1/2 hp 115volt blower motor here are the readings you should generally see:
Between White(common wire) and Black (high)- 6 ohms
Between White and blue (medium) - 9 ohms
Between White and red (Low) - 15 ohms
Between white and brown with white stripe(capacitor) - 0 ohms or very little
Between White and brown ( capacitor) - 45 ohms
Resistances will vary from motor to motor.
Also your motor may be a different horsepower along with the very distinct possibility that it may also have more speeds than I have shown .
If your motor differs from the one i show the resistances would be not be the same ,but as you can see , there is an increase in resistance as you go from the highest speed to the lowest speed. One of the Brown wires will always have little to no resistance and the other brown wire will have the highest resistance of all.
This will apply to all motors.
If your motor does not conform to this , it is BAD.
Ok, I did what you suggested and thanks so much for that. My readings are:
It's a 1/2 horse 115v 1075rpm 4 speed GE motor Part number (I think) is P918AS
Black = 2.8 ohms (High)
Blue = 3.4 ohms (M-High)
Yellow = 4.1 ohms (M-Low)
Red = 4.9 ohms (Low)
Brown /white stripe = 49.2
Brown = 5 ohms
Bad motor, eh?
Edited by Qball, 01 August 2011 - 08:09 PM.
#9
Posted 01 August 2011 - 08:42 PM
could be ..
you can test the Capacitor (somewhat) with an OHM meter
After discharging the Capacitor, use your OHM meter on the 20 Meg scale...
should start with a low reading and slowly rise.
Reverse the leads and try again ..
(may start with a "negative" OHMs and rise to 0 and then infinity)
My cap behaved exactly like this. So much for a cheap fix...
#10
Posted 01 August 2011 - 08:56 PM
#11
Posted 01 August 2011 - 10:00 PM
You are near big city . take a short drive and you should be able to get one at a good price locally. you should pay no more than $100 for that motor.
******It does not have to be a GE motor. Blower motors are almost universal.
This motor is VERY COMMON and not too expensive. I would include a link to ebay for a motor but Mr samurai seems to forbid ebay links. maybe Mr samurai should think about selling some HVAC parts if he is gonna stop links to ebay............................
Link to price compare site for your motor
Edited by ACtechGUY, 01 August 2011 - 10:13 PM.
#12
Posted 01 August 2011 - 10:09 PM
#13
Posted 02 August 2011 - 08:26 AM
#14
Posted 02 August 2011 - 04:36 PM
HIGH speed is used for cooling
Medium high or medium low can be used for Heat
Low speed is for constant fan.
More modern boards tend to have three outputs .This is where 4 speeds may be handy , but not really needed.
Modern boards will have a " cool" speed and "heat speed AND "constant" fan speed outputs. Most older control boards only have 2 motor outputs, heat and cool.
The extra speeds are for flexability . Say you wanted your heater to put out hotter air. You would choose MED- LOW or LOW speed on a 4 speed motor . Say you want to dehumidify a bit more , you would use a lower speed for cool.
But in reality , the differences between speeds is is not too much to be concerned about. you will not hurt anything by choosing Medium speed on a 3 speed motor when your old motor was hooked up to med -low.
Don't worry - -- Be happy
#15
Posted 04 August 2011 - 08:38 PM

What goes where?
edit: Sweet Georgia Brown. I get so worked up over nothing. I finally bothered to look at the label on the motor. All is well. Stupid rookie.
Edited by Qball, 04 August 2011 - 08:40 PM.
#16
Posted 04 August 2011 - 09:01 PM
.. Sweet Georgia Brown. I get so worked up over nothing.
one of my video productions: “Easter Seals: Walk With Me”
every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962
RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw
#17
Posted 04 August 2011 - 10:17 PM
Ha ha!! Thanks for that. It's fixed! Thanks for all the help everyone! I couldn't have done it without you.
1 user(s) are reading this topic
0 members, 1 guests, 0 anonymous users