Trane XL80 TUD100B948A0 - burner cycling while heating

Trane XL80 burner cycling

  • Please log in to reply
7 replies to this topic

#1 redlion4

redlion4

    Samanera

  • Grasshoppah
  • Pip
  • 5 posts

Posted 28 October 2011 - 09:32 AM

I have been observing an issue on our Trane XL 80 furnace where during operation, the burner cycles off frequently, but always relights within 20 seconds. Model number is TUD100B948A0, and yes, it is 20 years old this year - originally installed in 1991.

More specifics to the sequence of events, and "problem".
1. The thermostat calls for heat and the furnace turns on.
2. The exhaust fan turns on and shortly after that the burner lights.
3. The limit switch (Honeywell L4064A2881) can be observed as the it heats up - it passes the 80° "OFF" set point and continues to the 120° "ON" set point, at which time the blower fan turns on.
4. The temp reported on the limit switch then backs down and hovers around 100° while the blower operates. The LIMIT OFF is set point is set to 190°, but the switch never rotates up to this level during operation.

---> **Problem** <---
5. Out of the blue, the burner cuts off. One can hear the gas valve click off, cutting the gas supply to the burner, and see the flames go out.
6. Within 5 seconds, the control module clicks and the ignition begins to glow.
7. Within 20 seconds, the gas valve clicks back open and the burners relight.
8. The furnace continues to heat the house, noting that neither the exhaust fan nor the blower ever stopped during burner cycling.

9. Steps 5-8 repeat often (every 5-10 minutes?), until the thermostat reaches the set point and turns off the furnace.
10. Furnace shuts down as expected - burner off and exhaust fan off first (together), and the blower continues until the limit switch triggers the OFF set point of 80°.

Airflow does not appear to be an issue, given that the filter was just changed and the limit switch reports ~100° during operation, yet the problem still occurs. The control box red indicator light is not flashing at all, so it appears to be 'healthy'.

What is the correct order of troubleshooting at this point - inducer? flame sensor? exhaust flow? gas valve? other? And how does one go about checking these items? Voltage checks and/or ohm readings I can do. I do not own a manometer...at least not yet ;).

Thanks,
Ryan.

Use the Appliantology Parts Search Box to Find What You Need!
Enter your model number, part number, type of appliance, brand, or even a part description.
365-day return policy on all parts purchased here, even electrical parts that have been installed!

#2 Budget Appliance Repair

Budget Appliance Repair

    Sensei

  • Appliantology Fellow
  • PipPipPipPipPip
  • 4,887 posts

Posted 29 October 2011 - 05:33 AM

Sounds like the flame sensor getting flaky. If you have a flame sensor, (a metal rod about 1/8" in dia. with a ceramic mount on the opposite side of the hot surface ignitor - some use the hot surface ignitor as the sensor), take it out and clean it up good with steel wool and reinstall.

There's a high probability this will fix your problem.
William Burk (Willie)
Willie's Budget Appliance Repair
Eureka, CA 95501

#3 redlion4

redlion4

    Samanera

  • Grasshoppah
  • Pip
  • 5 posts

Posted 29 October 2011 - 03:18 PM

Located the flame sensor this morning. Removed it and gave it a good cleaning. Had not done that since we have lived here - 8 years. Actually doubt it has ever been cleaned. I will continue to watch / listen to the furnace to see if the cycling reoccurs and report back soon :). Thx!

#4 redlion4

redlion4

    Samanera

  • Grasshoppah
  • Pip
  • 5 posts

Posted 31 October 2011 - 09:12 AM

Monday update:

Cleaned the flame sensor, and the problem still occurs. The pressure switch reports open with 24 VAC when the burner kicks out, then moves back closed (0 VAC) as the ignition turns on and burner relights.

Just did the pressure switch test quickly this morning. Found, but did not write down nor take a photo of, the pressure switch sticker with model number and specs. Will snap a photo of it tonight and research it.

Next question - how does one determine if the pressure switch is 'bad' versus it is detecting a true problem with the exhaust? Is the appropriate action to first replace the pressure switch, then if the problem continues to troubleshoot the exhaust venting? Or are there different things that can be verified with the exhaust system?

Thanks again,
Ryan.

#5 redlion4

redlion4

    Samanera

  • Grasshoppah
  • Pip
  • 5 posts

Posted 04 November 2011 - 08:33 AM

Jumpered out the pressure switch for ~40 minutes while I watched the furnace heat the house 5°. No burner cycling occurred with the pressure switch bypassed.

So either the pressure switch is going flaky, or an actual problem exists with the inducer / furnace box. Pressure switch is a Tridelta FS6322-441. Looks like it resolves to SWT02291. Rather difficult to find that part online, or so it appears...

Suggestions on how to proceed?

#6 RegUS_PatOff

RegUS_PatOff

    Sensei

  • Academy Instructor
  • PipPipPipPipPip
  • 33,588 posts
  • Location: USA
  • Flavorite Brew:Chief NTSC Black & White

Posted 04 November 2011 - 12:13 PM

Rather difficult to find that part online, or so it appears...

http://www.expertapp.../partfinder.php $ 269 :woot:

eBay, used :kopkrab: $ 35
.

one of my video productions: “Easter Seals: Walk With Me”

every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962

RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw

#7 redlion4

redlion4

    Samanera

  • Grasshoppah
  • Pip
  • 5 posts

Posted 04 November 2011 - 02:32 PM

http://www.expertapp.../partfinder.php $ 269 :woot:

eBay, used :kopkrab: $ 35

Funny thing you saw that eBay listing. Yesterday there were two available, today there is one. The sold one arrived in our mailbox today ;). It is worth $35 to try, given the high feedback rating and that Rochester is only a few hours from our house.

If the problem continues with the replacement switch in place, I'll be opening the furnace to have a peek at the inducer and core. Most likely, this course will lead to a new furnace rather than repairing a 20 year old one...

#8 Shootist

Shootist

    Yamabushi

  • Appliantologist
  • PipPip
  • 60 posts

Posted 04 January 2012 - 09:04 PM

Did you check the thermostat? If digital replace the batteries first. Take the red and white wires loose on the thermostat and twist them together. If that solves the problem then replace the stat. If there was a problem with the pressure switch, limits or flame sensor you should have seen an error code. If you're getting a weak signal from the stat I've seen the exact symptoms without ever seeing an error code.




0 user(s) are reading this topic

0 members, 0 guests, 0 anonymous users


FAQs | Store | Memberships | Repair Videos | Academy | Newsletter | Beer Fund | Contact


Use the Appliantology Parts Finder to Get What You Need!
Enter a model number, part number, type of appliance, brand, or even a part description.
365-day return policy on all parts purchased here, even electrical parts that have been installed!