Carrier 58SXA060100GG Furnace - Inducer runs but no spark or pilot

21 posts in this topic

My furnace worked last week, but this week it no longer fires up.

When I set the thermostat to call for heat, the inducer fan starts but the pilot never sparks. The inducer runs for a few minutes and then shuts down. I would like to figure this out since I have some time but have not made in progress over last couple days searching the internet. Thanks.

Norm

Share this post


Link to post
Share on other sites

Need appliance parts? Call 877-803-7957 now!

does the Pilot Gas Valve open ?

Share this post


Link to post
Share on other sites

I don't hear a click that would indicate pilot gas valve opening, but it could be hidden by the inducer noise. Is there a simple test to see if the pilot gas valve operates?

Share this post


Link to post
Share on other sites

should be able to "feel" the Gas Pilot Valve open, and / or smell the Gas

Check the thermal Fusible Link Fuse on the Yellow wire that connects to the Gas Valve and the Spark Generator

1 person likes this

Share this post


Link to post
Share on other sites

RegUS, I separated the molex before and after fusible link yesterday and found continuity across fusible link. I will go put my finger on the gas valve and call for heat to see if there is a click. I have not smelled gas but let me put nose closer.

Share this post


Link to post
Share on other sites

I don't feel a click with my finger on the gas valve. I don't smell gas. The gas could be getting exhausted by the inducer fan. What next?

Share this post


Link to post
Share on other sites

check the Pressure Switch (and it's tubing)

Common - Yellow

Normally Closed - Orange

Normally Open - Brown

1 person likes this

Share this post


Link to post
Share on other sites

Blow through the tubing to make sure the vacuum between the switch and the inducer is clear.

Share this post


Link to post
Share on other sites

I did the pressure switch. NO and NC ok. Blew into hose and actuated pressure switch. Both sides changed state. Blew into hose from pressure switch to inducer. Air moving. Also found continuity on the temp limit switch behind the gas valve.

Share this post


Link to post
Share on other sites

If the Pressure Switch is activated, there should be 24v AC (measured to ground) at the

Gas Valve

4 Yellow

5 Brown

Share this post


Link to post
Share on other sites

Noob question. Do I remove the connector and probe gas valve tab to ground or do i probe connector to ground?

Share this post


Link to post
Share on other sites

Yellow connector at gas valve has 26.7v. Brown connector is 0v.

Share this post


Link to post
Share on other sites

either the Fuse is blown or a bad Flame Sense Switch:

24v AC at Yellow

24v AC at Green

24v AC at White (only when there's Flame)

Share this post


Link to post
Share on other sites

At connector PL5 feeding into the PIL I found

26v at yellow

0v at brown which feeds green into the PIL

0v at white

The 26v at yellow proves the Fusible link. I think.

Strange but also found 3.5v at yellow before touching to ground. Only did this on yellow not other brown and white connections. What do you think.

So would the 0 v at brown feeding the gas valve and 0 v a brown feeding green into the PIL indicate a problem with the Ignitor?

Thanks for your help.

Share this post


Link to post
Share on other sites

(make sure the Brown / Green wires aren't shorted to ground)

You could disconnect PL5, and there should be continuity between Yellow and Green, if not, bad PIL

Jumper Yellow to Brown on (still disconnected) PL5, and you should get Sparks at your Ignitor and get Pilot Flame

Share this post


Link to post
Share on other sites

Checked and found both sides of PL5 brown and green not shorted to ground.

Disconnected PL5 and found no continuity between Yellow and Green on PIL side. So bad PIL.

Jumped Yellow to Brown on ILO/GV side, powered furnace, after 15-20sec sparker started and pilot lit and maintained blue flame. I then cancelled thermostat after 10sec before unit fired up.

So I need a new PIL? Can you help with part number to search. Recommend source.

Also any instructions on correct procedure to replace PIL assembly or do you just figure it out.

Looks like I have to disassemble the bottom of the fire box and remove gas fitting and couple of screws.

Nice job Sensei.

Share this post


Link to post
Share on other sites

sorry, I don't know anything about that Furnace :whistling:

just what I found on internet searches...

PIL part number may be

LH-680-005

LH680005

Sears $ 140

eBay $29 used

$40 +$7 new

Do a search for each of those part numbers

There was a "old" class action lawsuit or something on the Heat Exchanger on that Furnace ..

http://hipspro.com/pubs/Furnace-clasaction-detailed_notice.pdf

Share this post


Link to post
Share on other sites

Is THIS you?

Share this post


Link to post
Share on other sites

Is THIS you?

$ 180 :woot:

Share this post


Link to post
Share on other sites

Thanks. "This" must be the ouch price. Man those guy must love using the markup calculator.

Can you clean these things and get them working again or are they normally shot to sh*t?

Can you reuse the sparker or do you I need a new one also?

Share this post


Link to post
Share on other sites

The Ignitor should be OK..

You may be able to open the b ox and take a look at the switch ...