AMANA GUID090EA50

10 posts in this topic

This furnace led blinks continuously and the the burner lights but goes right back out. My friend changed the flame sensor but no help. Any ideas beside main board????thanks in advance

Edited by hawgwildtours

Share this post


Link to post
Share on other sites

Need appliance parts? Call 877-803-7957 now!

This furnace led blinks continuously ...

continuously, ?

OR repeats a certain number of flashes ?

Share this post


Link to post
Share on other sites

I was wondering the same thing. I will go by his house tonight and see

Share this post


Link to post
Share on other sites

I just called him and he says it is continuos

Share this post


Link to post
Share on other sites

Continuous flashing on the LED might mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram

Edited by applianceman18007260692
1 person likes this

Share this post


Link to post
Share on other sites

AMANA & GOODMAN FAULT CODES

1. One led flash that stays on continuously = No signal from thermostat. Turn off power and check connections.

2. One led that flashes = Furnace lockout after three attempts to fire. Must be reset by lowering it for twenty seconds and then raise it back. After one hour furnace will reset itself.

3. Two led flashes = Draft Inducer not working or shorted or failed pressure switch.

4. Three led flashes = Open pressure switch.

5. Four led flashes = open primary limit switch due to faulty wiring or bad filters.

6. Five led flashes = Sensing flame without a call for heat due to possible slow closing valve.

7. Seven led flashes = faulty flame sensor

8. Eight led flashes = faulty igniter

9. Continuous led flashing = Reverse polarity. Check wiring diagram

2 people like this

Share this post


Link to post
Share on other sites

My friend had changed the igniter instead of the sensor. I cleaned the sensor and all is well. As for the blinking light this furnance was wired with 2 thermostats for a two story house and they used two boards. There was a green led on the add on board but it was saying normal operation. Main board did not have power to it until downstairs called for heat. Thanks again for all help

Share this post


Link to post
Share on other sites

My friend had changed the igniter instead of the sensor. I cleaned the sensor and all is well. As for the blinking light this furnance was wired with 2 thermostats for a two story house and they used two boards. There was a green led on the add on board but it was saying normal operation. Main board did not have power to it until downstairs called for heat. Thanks again for all help

Two boards for one furnace? Never seen that before.

Share this post


Link to post
Share on other sites

When getting a flame sensor error always make sure the furnace is properly grounded before you do anything else. An ungrounded furnace will pull a little ground off of the gas line but this is not a good ground source and the furnace will work when it feels like it and drive you up a wall. If the ground is good then cleaning the sensor rod with a little steel wool or fine grit sandpaper will usually fix it.

I had a customer once that had a heater problem. Every fall their previous A/C guy had to come out and replace the flame sensor. This went on for years and finally they got fed up and called me instead. I knew right away the problem once I saw the old 2-prong socket in the attic. Luckily the water heater was close by so I ran a new ground wire to a ground clamp on the cold water line and the furnace fired right up. The following fall I got a "thank you" card from this customer because it was the first time in years the furnace worked right the first cold spell.

1 person likes this

Share this post


Link to post
Share on other sites

I know this might be a little late coming, but I had the same problem with your model last Spring. A closer look revealed a pressure switch (round diagpham cannister looking thing with small hose attached to it) that was tripping off prematurely. The Draft Induced Blower (first thing to start in the forced air heating cycle, purges exhaust gases to exterior) has a purpose-built hose nipple to send positive air pressure down that small hose via the spinning fan in the DIB....be it ever so small CFM of air movement.

Problem is, if anything is compromised in that small air signal to the pressure switch, the diaphram plunger pintle will not extend far enough to comletely and consistently trip (close the contacts) in the lever microswitch (mounted on one side of the pressure swith pot) to send the signal the controller (LED box) wants to see. Any interruption/failure in the pressure switch tells the Controller the Draft Induced Blower is not running (even if it is) --which is an UNSAFE condition and the entire heating cycle process comes to an abrupt halt.

So, what you've got is a weak air signal to the pressure switch, which can be caused by:

--ruptured/torn rubber hose from DIB to Pressure Switch

--tired DIB spinning at lower rpm's creating less air movement than needed

--an "air leak" somewhere in the intake/exhaust manifolds for the DIB

--a faulty and/or leaking pressure switch

I finally found a new DIB on Ebay (they're very expensive) for my Amana just like yours, but that still didn't cure the problems like you're experiencing. It wasn't until I played with bending the microswitch metal mounting tab on the pressure switch that I could affect a changed relationship of the air signal/pintle engagement at the microswitch that made the big difference. It was very tricky positioning that arc of bend in the tab just right, but after much patience and testing, I finally got it right. You have to be very careful though by bending the tab only micro-inches at a time in your trial-and-error process---too much bend and the furnance cycle gets befuddled by the sequence of the switch contact cycle.

Just don't let any appliance parts salesmen talk you into buying one of those "Adjustable Pressure Switches" if you decide to replace yours instead (it may still need tweaking anyway). The adjustables are not only junk, they never operate consistently and will confuse your furnace even more! I know...I tried one.

1 person likes this

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!


Register a new account

Sign in

Already have an account? Sign in here.


Sign In Now