When it calls for heat most of the time fan kicks on and pushes warm air out of the vents. Sometimes the fan does not come on, sometimes the fan cuts off while still on the heat cycle with few degrees shy of where the thermostat is set.
In either non function situation the thermostat has "heat on" the displayed and red LED is lit up on the control panel outside of the air handler that shows heat is energized.
Fan comes on and stays on during all A\C cycles.
Any ideas of where the problem maybe?
#2
Posted 24 December 2011 - 07:41 AM
How many wires on the fan motor and where are they connected?
Your motor should have a black motor wire connected for high speed for cooling.
It may have a red or blue wire connected for low or medium speed heat.
The lo or med. speeds could be bad or a bad wire connection.
The fan relay could be bad in the lo or med. relay switch.
Your common wire will be white yellow or purple.
Leave it alone.
If red or blue is connected,remove them and tape the terminal ends so they do not short out.
Put the black wire in the terminal the red or blue was in and run the heater and let us know what happens.
- Samurai Appliance Repair Man likes this
#3
Posted 24 December 2011 - 07:45 AM
If so the limit switch could be bad or a heater limit could be bad.
Attach your amp meter to the system while running in heat.
Each heater will pull about 18-20 amps.
Edited by jumptrout, 24 December 2011 - 09:03 AM.
- Samurai Appliance Repair Man and kdog like this
#4
Posted 24 December 2011 - 10:24 AM
3 wires come out of the fan, yellow to a transformer, black to relay on control board, blue not attached.
The heat coils are pullign amps dont know how much, wires get very warm.
I'll get some pics of the setup.
#5
Posted 24 December 2011 - 10:56 AM
http://i307.photobuc.../DSC03168-1.jpg
http://i307.photobuc...C2/DSC03169.jpg
http://i307.photobuc...C2/DSC03170.jpg
http://i307.photobuc...C2/DSC03168.jpg
http://i307.photobuc...C2/DSC03167.jpg
http://i307.photobuc...C2/DSC03166.jpg
http://i307.photobuc...C2/DSC03165.jpg
http://i307.photobuc...C2/DSC03164.jpg
#6
Posted 24 December 2011 - 11:44 AM
One set for amps and attached to the air handler power supply to read heater amps.
The other set for volts to check yellow and black on the motor at the transformer and the fan relay.
These should be checked simultaneously.
If voltage to the motor stops and the heaters continue heating I would replace the control board.
In the interim you should use FAN ON at the thermostat while in the heat mode to avoid a possible malfunction in the heaters.
- Samurai Appliance Repair Man and kdog like this
#7
Posted 24 December 2011 - 12:13 PM
A couple of itmes to add I replaced the control board and fan motor capacitor.
Something drawing down the amps to keep the fan from starting?
#8
Posted 24 December 2011 - 01:02 PM
Amp the heaters.
Amp the motor.
Check board power(volts) to the motor.
Check the green (fan) signal at the board from the t-stat.
Verify your re-wiring of the new board to the wiring diagram.
All these have to be done at the same time to find out what is malfunctioning.
- kdog likes this
#9
Posted 24 December 2011 - 01:17 PM
check the specs ... red "clamp" is OK,
don't get the meter with the "pink" Clamp
(also usually 20% OFF coupons somewhere, even on sale items)
- kdog likes this
one of my video productions: “Easter Seals: Walk With Me”
every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962
RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw
#10
Posted 24 December 2011 - 06:07 PM
- kdog likes this
"May the hinges of our friendship never grow rusty"
-old Irish saying
Buy me a Beer: http://web.me.com/ze...man18007260692/
#11
Posted 24 December 2011 - 09:09 PM
If a heater coil starts to go bad it can draw to much current and keep other timed devices from starting?
On the single stack timing sequencer the smaller gauge blue wire goes to the control board relay it turns it on for the fan motor?
thanks and Merry ChristmasHappy Holidays.
#12
Posted 24 December 2011 - 11:42 PM
"May the hinges of our friendship never grow rusty"
-old Irish saying
Buy me a Beer: http://web.me.com/ze...man18007260692/
#13
Posted 25 December 2011 - 02:23 AM
#14
Posted 25 December 2011 - 11:10 AM
It does heat not as fast when both heat coils are plugged in.
Something drawing to many amps?
heat coil going bad? fan motor?
#16
Posted 25 December 2011 - 02:43 PM
- kdog likes this
"May the hinges of our friendship never grow rusty"
-old Irish saying
Buy me a Beer: http://web.me.com/ze...man18007260692/
#17
Posted 25 December 2011 - 08:34 PM
#18
Posted 26 December 2011 - 07:58 AM
If the motor still has power it will be a bad motor.
What is the amp draw on the motor?
#19
Posted 26 December 2011 - 11:52 AM
"May the hinges of our friendship never grow rusty"
-old Irish saying
Buy me a Beer: http://web.me.com/ze...man18007260692/
#20
Posted 27 December 2011 - 09:20 PM
heat coil 1
start 16
run 15
heat coil 2
start 17
run 15
fan black wire
start 3.5
run 2.2
fan capacitor brown wire
run 1.75
One thing I did notice with second person at the thermostat once I plugged in the 2nd heat coil I previously unplugged, "heat on" would light up on the thermostat and heat light illuminated on the air handler control panel afixed to the outside of it. But no heat would come on, fan or coils varified with amp gauge. The unit had ran 2 minutes prior with one heat coil plugged in. I unplugged 2nd heat coil again plugged in power breaker set thermostat for heat call and everything turned on.
0 user(s) are reading this topic
0 members, 0 guests, 0 anonymous users
FAQs | Parts | Memberships | Repair Videos | Newsletter | Beer Fund | Contact
Your Sometimes-Lucid Host:
"If I can't help you fix your appliance and make you 100% satisfied, I will come to your home and slice open my belly,
spilling my steaming entrails onto your floor."
ApplianceGuru.com | AppliancePartsResource.com | Fixitnow.com