York H2RC048S06A Fan Needs Push, But Already Replaced Parts
#21
Posted 13 April 2012 - 08:02 PM
What were the symptoms of your "old" Fan ?
one of my video productions: “Easter Seals: Walk With Me”
every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962
RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw
#22
Posted 13 April 2012 - 08:48 PM
Seriously though, to sum it up...
Requirements:
1. It needs 220 or so volts (and be capable of maintaining voltage under load) across both the run (red) & common (black) and start (brown) & common (black). <<<<< Or the wiring or other electrical component is the problem.
2. It needs a good capacitor of the correct mfd rated FOR THE MOTOR INSTALLED (on the brown wire) AND capacitor has to be good under a load. Once in awhile they can test fine and still not be good enough under load. This capacitor can be one side of a dual or it can have a single cap for the fan and a single cap for the compressor. <<<<<< Or the capacitor is the problem.
3. Windings need to check out good. <<<<< Or the motor is the problem.
4. Bearings and other such mechanical things need to be working and free / unobstructed. <<<<< Or the motor / fan etc is the problem. Check amp draw on fan when you have it spinning (with a clamp meter if you have the capability). If it is high (over the rated 1.3 amps, it might indicate bearings or such issues. note though: a bad cap can raise amp draw as well)
If it doesn't work after all that, u maybe missed something. Time to punt.
Edited by Bullstok, 13 April 2012 - 09:29 PM.
- Samurai Appliance Repair Man likes this
#23
Posted 14 April 2012 - 12:55 AM
The old fan would make loud screeching noises. It was replaced roughly a year ago and the unit has worked well with the replacement fan, up until the last week or so. I'm pretty bummed that the new fan didn't make it very long, guess "Made in Mexico" doesn't mean what it used to....or the way it's wired ...
What were the symptoms of your "old" Fan ?
#24
Posted 14 April 2012 - 12:58 AM
It's the model A fan motor. It is crank start. Update ur motor.
Seriously though, to sum it up...
Requirements:
1. It needs 220 or so volts (and be capable of maintaining voltage under load) across both the run (red) & common (black) and start (brown) & common (black). <<<<< Or the wiring or other electrical component is the problem.
2. It needs a good capacitor of the correct mfd rated FOR THE MOTOR INSTALLED (on the brown wire) AND capacitor has to be good under a load. Once in awhile they can test fine and still not be good enough under load. This capacitor can be one side of a dual or it can have a single cap for the fan and a single cap for the compressor. <<<<<< Or the capacitor is the problem.
3. Windings need to check out good. <<<<< Or the motor is the problem.
4. Bearings and other such mechanical things need to be working and free / unobstructed. <<<<< Or the motor / fan etc is the problem. Check amp draw on fan when you have it spinning (with a clamp meter if you have the capability). If it is high (over the rated 1.3 amps, it might indicate bearings or such issues. note though: a bad cap can raise amp draw as well)
If it doesn't work after all that, u maybe missed something. Time to punt.
Thank you for the excellent summary. That makes sense, I'll give another fan a shot and if that doesn't fix it, call in some expert eyeballs to give things a look. Are there better quality replacement fans that offer a longer service life than the AO Smith F48J66A48 that is in the unit?
#25
Posted 14 April 2012 - 01:28 AM
service call may cost as much as a new Fan Motor and Capacitor plus parts... that doesn't fix it, call in some expert eyeballs to give things a look.
For a Capacitor, you could buy just a 5 uF one (much cheaper than the dual)
Try that first, if no-go ... time for a new Fan Motor
- Samurai Appliance Repair Man likes this
one of my video productions: “Easter Seals: Walk With Me”
every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962
RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw
#26
Posted 14 April 2012 - 07:18 AM
If it wasn't and the new motor called for a different capacitor rating, what would the ramification be to the new motor
and/or the old capacitor if it was in-fact able to make it start and run correctly for the last year that it has been working?
- Samurai Appliance Repair Man likes this
Willie's Budget Appliance Repair
Eureka, CA 95501
#27
Posted 14 April 2012 - 09:28 AM
A word of warning for anybody else....stay away from chinese HVAC parts; especially anything labeled "Packard".
- Samurai Appliance Repair Man likes this
#28
Posted 14 April 2012 - 10:35 PM
? I Wonder if the existing dual capacitor was rated correctly for the new motor that was installed a year ago?
If it wasn't and the new motor called for a different capacitor rating, what would the ramification be to the new motor
and/or the old capacitor if it was in-fact able to make it start and run correctly for the last year that it has been working?
The replacement motor was the same make/model as the original and the new and old caps were the same exact rating. Granted, something could have been defective, but I was careful to match the specs on the labels. Certainly worth mentioning, though.
#29
Posted 14 April 2012 - 10:38 PM
Did you remove the drain plugs from the down-facing (shaft) side of the motor? I've seen many motors fail in their first year because the drain plugs weren't removed. If the capacitor is good the motor has to be bad (assuming you wired it correctly). If you replaced a 3-wire motor with another 3-wire motor you can't get it wrong.
A word of warning for anybody else....stay away from chinese HVAC parts; especially anything labeled "Packard".
The bottom of the motor has two holes in it, but no plastic plugs of any kind that I could see. The motor has a wiring harness connector, that plugs only one way into the rest of the unit, so it wouldn't be possible to wire it wrong, as it is "plug and play".
Is there a better replacement motor than the AO Smith F48J66A48 that is in the unit?
#30
Posted 16 April 2012 - 07:58 PM
As for the quality of that motor? Most manufacturers aren't going to spend top dollar on an OEM fan motor. AO Smith makes a decent motor. Make sure rain water isn't pouring down directly onto your motor.
Edited by Shootist, 16 April 2012 - 08:00 PM.
- Samurai Appliance Repair Man likes this
0 user(s) are reading this topic
0 members, 0 guests, 0 anonymous users
FAQs | Parts | Memberships | Repair Videos | Newsletter | Beer Fund | Contact
Your Sometimes-Lucid Host:
"If I can't help you fix your appliance and make you 100% satisfied, I will come to your home and slice open my belly,
spilling my steaming entrails onto your floor."
ApplianceGuru.com | AppliancePartsResource.com | Fixitnow.com