Jump to content
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 27 April 2024 02:00 PM Until 03:00 PM
      5  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological. 
      We have a special session planned for this one. Instead of the usual Show 'n Tell on a technical topic, we're going to post tech sheets in the comments to this Calendar Event (scroll down to see what's posted so far) and ask specific questions that can only be answered by reading the tech sheet. If you at least try to answer the questions beforehand, you'll get a lot more out of it. The tech sheet and the questions are posted in the comments section below.
      Your mission, if you should choose to accept it, is to check out the questions for each one and try to answer them ahead of time. Then come to the Dojo to see how well you did! 
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, April 27 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Gibson GR4GA package unit - contactors won't pull in


jb8103

Recommended Posts

When calling for AC, the contactors do not pull in. The indoor blower motor does come on. If I manually actuate the contactor then the compressor/condenser fan energize.

I replaced the contactor. Same problem.

There is 24 volts going to the coils.

Link to comment
Share on other sites

  • Replies 4
  • Created
  • Last Reply

Top Posters In This Topic

  • jb8103

    3

  • RegUS_PatOff

    1

  • jumptrout

    1

Top Posters In This Topic

... There is 24 volts going to the coils.

... measured voltage with the Coil still connected ?

Link to comment
Share on other sites

... measured voltage with the Coil still connected ?

Yes, but I will double check tonight. I was a bit casual last night.

I have the wiring diagram PDF but don't know a good fileshare site offhand.

Edited by jb8103
Link to comment
Share on other sites

Disconnect the thermostat wires from the unit.

Use a jumper wire at the low voltage terminal board to jump ® red to (Y) yellow.

If the contactor closes you will have to look at the thermostat wire and or thermostat for your problem.

If you have a digital thermostat there is a 5 minute delay from turning on power until yellow will close.

Link to comment
Share on other sites

It's the anti-short cycle timer (stock for this unit), I'm pretty sure now. There is a Lux digital thermostat but the power stays on for hours and still nothing. I was wrong about 24V going to the contactor, there is no power at the contactor. There is 24V going to the timer, but nothing coming out.

How I missed that the first time I don't know but I think it says something about twelve-hour days.