Can someone please help me verify the correct capacity for the motor run capacitor for two HVAC units that I have, please? I believe the AC service technician replaced BOTH units with the WRONG capacitor size.
AC Unit # 1
Lenox 10HPB42-11P
Capacitor – I believe this should be a 40+5 MFD capacitor
Service technician installed a 50+7.5 MFD capacitor
AC Unit # 2
Carrier
Prod: 38CKC048-371
Model: 38CKC048370 / 38CKC48370 / 38CK048370 (???)
Service technician installed a 40+3 MFD capacitor
Thank you,
Cameron
  • Replies 10
  • cninham
  • jumptrout
  • m_west5
Fan Motor Capacitor rating is dependent on actual Fan Motor installed.
Thank you for the reply -- in both cases the fan motor is the original motor and the AC unit is "standard" with nothing changed.
Any idea where I can get the capacitor information from, please?
Thanks -- Cameron
The fan motor will have the cap rating printed on it.
Thanks -- I got the fan motor capacity rating from the motor as suggested.
How do I get the compressor (HERM) capacitor rating?
Cameron
my research finds:
AC Unit # 1
Lennox 10HPB42-11P
80K48 40/5 440v
AC Unit # 2
Carrier
38CKC048370
P291-5054RS 50/5 440v
Thank you! Very much appreciated!
On the 2nd unit, the Carrier, Prod: 38CKC048-371, Model: 38CKC048370, I have received conflicting information. Some other forums have stated the capacitor to be:
45+5 MFD, 440 VAC
Would the discrepancy/difference between the two matter? Is it safer to go with the 45+5 or 50+5 MFD...?
Thanks -- Cameron
The 10% mentioned by Reg is good info.
The real important part is the 370vac/440vac capacitor.
Any system can run fine with a 440vac.
If a system specifies 440vac it will not run correctly on a 370vac.
  • 10 months later...
I know this is an old posting, but may help someone else reading it.  It's a pain to do, but to be absolutely sure of the capacitance for the compressor, you could remove fan from top of condenser unit and look at the sticker on the compressor. Most Copeland scrolls (very common) and other mfg's have the cap rating on this sticker.
Hope this helps.