Intertherm condensor intermittent
#1
Posted 12 July 2012 - 10:02 AM
I wish I could provide more info on the model of the unit but the information tag on the outside of the unit has almost completely faded. Anyone have any ideas?
#2
Posted 12 July 2012 - 11:02 AM
could be ...... Is there a chance that the relay is just weak and it is a coincidence that it works after the thermostat has been pulled for a few minutes
Does the outside Relay energize when calling for cooling ?
Does the Compressor try to start or make any noises ?
Does the Outside Fan run at that time ?
one of my video productions: “Easter Seals: Walk With Me”
every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962
RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw
#3
Posted 12 July 2012 - 11:07 AM
#4
Posted 12 July 2012 - 12:01 PM
is there 24vDC at the Relay Coil Terminals when there should be ?
one of my video productions: “Easter Seals: Walk With Me”
every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962
RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw
#6
Posted 12 July 2012 - 02:59 PM
If this is a heat pump with a defrost control board in the condensing unit you can locate the red incoming thermostat wire connection on the board.
Remove then replace the wire. If the unit comes on you need to replace the defrost control board.
#7
Posted 12 July 2012 - 03:05 PM
in this picture I have 24v at the when I read from the yellow to the black wire (the wires that come from the thermastat) nothing at the red wire (all when unit is calling for the compressor)
If I read this schematic right the circuit card above is a time delay and when the thermastat calls for the unit to come on I should have 24v at the red wire correct?
or am I just all messed up?
I currently cannot get the unit to work to see if it is getting 24v when it works correctly.
if I am supposed to have 24v at the red wire coming off that time delay and I do not then that should be what is wrong correct?
#8
Posted 12 July 2012 - 03:17 PM
may be a weak Relay / Contactor
is there 24vDC at the Relay Coil Terminals when there should be ?
sorry it took so long I had to get home to double check before answering, the answer is no! At least not right now! If I can get it to come on again I will learn a lot more ( I THINK )
#9
Posted 12 July 2012 - 03:22 PM
The time delay relay can be eliminated due to the digital thermostat.
The thermostat has a time delay built in to it.
Take the red and black wire off the board and wire them directly to the 2 incoming thermostat wires.
When the stat it set to cool and is not in a time delay mode you should have 24 volts at the condenser on what appears in your photo as red and white.
If you do not have 24v there you have a stat problem or a wire problem.
#10
Posted 12 July 2012 - 03:22 PM
You could try removing (and bypassing) the Time Delay from the circuit ..
You shouldn't run it that way much, because if the Compressor tried to start right after it stopped (no time delay)
it could hurt the Compressor.
edit> OR what ^he^ said
one of my video productions: “Easter Seals: Walk With Me”
every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962
RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw
#11
Posted 12 July 2012 - 03:26 PM
By the way jumptrout it is not a heat pump unit.
#12
Posted 12 July 2012 - 03:30 PM
The wall Thermostat may have a built-in time delay...
model number ?
one of my video productions: “Easter Seals: Walk With Me”
every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962
RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw
#13
Posted 12 July 2012 - 03:42 PM
hard to read, but yes, I think so...
You could try removing (and bypassing) the Time Delay from the circuit ..
You shouldn't run it that way much, because if the Compressor tried to start right after it stopped (no time delay)
it could hurt the Compressor.
edit> OR what ^he^ said
ok so once it finally broke for good it helped with the troubleshooting! I took the delay out of the system and it works, The question I have is should I replace the time delay on the condensor unit or will the one that is in the digital thermastat protect the unit?
If I do need to replace the one on the unit can anyone tell me what I should buy? Are they generic?
Oh yeah and THANK YOU for the help! I really hope I can re-pay it somehow in the future!
#14
Posted 12 July 2012 - 04:08 PM
Any part numbers on the Time Delay ?
The wall Thermostat may have a built-in time delay...
model number ?
one of my video productions: “Easter Seals: Walk With Me”
every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962
RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw
#15
Posted 12 July 2012 - 04:19 PM
#16
Posted 12 July 2012 - 04:25 PM
you should be OK without the Time Delay Board
one of my video productions: “Easter Seals: Walk With Me”
every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962
RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw
0 user(s) are reading this topic
0 members, 0 guests, 0 anonymous users
FAQs | Parts | Memberships | Repair Videos | Newsletter | Beer Fund | Contact
Your Sometimes-Lucid Host:
"If I can't help you fix your appliance and make you 100% satisfied, I will come to your home and slice open my belly,
spilling my steaming entrails onto your floor."
ApplianceGuru.com | AppliancePartsResource.com | Fixitnow.com