Could someone please comment. Is it necessary to evacuate the freon from the system even though the A/C it's going to be reused.
Thanks,
#2
Posted 17 July 2012 - 11:45 PM
"May the hinges of our friendship never grow rusty"
-old Irish saying
Buy me a Beer: http://web.me.com/ze...man18007260692/
#3
Posted 18 July 2012 - 12:15 AM
The Evaporator Coils are inside the house, inside the Furnace Air Handler
How are you going to take either or both without disconnecting them ?
one of my video productions: “Easter Seals: Walk With Me”
every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962
RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw
#4
Posted 18 July 2012 - 11:54 AM
#5
Posted 18 July 2012 - 12:23 PM
Start the system in COOL.
Once the suction pressure starts pulling down,CLOSE the high side valve.
When the low side gets to "0" psi quickly close the suction valve and DISCONNECT power.
Cut your copper refrigerant lines near the condenser and seal the cut lines with tape.
Same for the inside lines at the air handler.
When the unit has been re-installed add a filter drier to the high side tubing, pull a good vacuum on the lines and the A/H..
If no leaks are present,open the high side valve to release the captured refrigerant.
Then open the low side valve.
0 user(s) are reading this topic
0 members, 0 guests, 0 anonymous users
FAQs | Parts | Memberships | Repair Videos | Newsletter | Beer Fund | Contact
Your Sometimes-Lucid Host:
"If I can't help you fix your appliance and make you 100% satisfied, I will come to your home and slice open my belly,
spilling my steaming entrails onto your floor."
ApplianceGuru.com | AppliancePartsResource.com | Fixitnow.com