Jump to content
Click here to check out this guide.

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 27 April 2024 02:00 PM Until 03:00 PM
      5  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological. 
      We have a special session planned for this one. Instead of the usual Show 'n Tell on a technical topic, we're going to post tech sheets in the comments to this Calendar Event (scroll down to see what's posted so far) and ask specific questions that can only be answered by reading the tech sheet. If you at least try to answer the questions beforehand, you'll get a lot more out of it. The tech sheet and the questions are posted in the comments section below.
      Your mission, if you should choose to accept it, is to check out the questions for each one and try to answer them ahead of time. Then come to the Dojo to see how well you did! 
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, April 27 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Excess condensation


patcap38

Recommended Posts

My central AC unit all of the sudden began producing excess condensation from the coils which is leaking into the secondary catch pan in the attic and running out of the attic drain to the outside of the house. A week prior I had a service tech out to add freon but he was not able to locate a leak at that time. He did look in the blower unit and in the coils for the leak. Can anyone offer a possible cause for this new development? Thanks.

Link to comment
Share on other sites

  • Replies 1
  • Created
  • Last Reply

Top Posters In This Topic

  • patcap38

    1

  • jumptrout

    1

Top Posters In This Topic

Excess may or may not be excess.

Check and clear the primary drain line,it could be stopped up.

The primary drain pan under the coil may have a crack in it.

A shop vac on the drain line from the outside of the house works good.

Check the air handler panel for loose or missing screws and a tight seal.

Excess humidity from the attic ditectly into the air handler causes excess condensate.

Check the incoming side of the evaporator coil for dirt and dust.

A dirty coil and or dirty blower wheel blades can cause this.

Loose ductwork at the return plenum must be resealed.

Low refrigerant usually results in a frozen coil not excess condensate.