Troubleshoot problem with Ruud A/C
#1
Posted 06 August 2012 - 05:27 PM
Took the unit apart and got it to the point where the compressor was working but the fan was not spinning (I pressed the button labeled "High Pressure Control Release/Reset" though I'm not sure if pressing this button was what got the compressor turned on or not). Got the fan to spin manually, so figured the issue was just the capacitor.
Replaced the capacitor (original was 40/3 but the store had only 40/5, which they said would work) but now I can't get anything to turn on - either the compressor or the fan.
Is there a good way to troubleshoot what other parts may need to be replaced?
One other thing - when I first went to replace the capacitor, for some reason, there was still electricity going to the A/C even though I had turned off the breaker. I managed to get some sparks before I realized this and turned off the main feed to the house. Is it possible I shorted something or fried one of the electrical parts? Any good way to test what needs to be replaced?
Thanks.
Here are the relevant pictures (last one is of the unit with the replacement capacitor installed. It was smaller in diameter than the old one, so I needed to fill with some weather stripping.) The "reset" button is the red one at the bottom center of the first picture.
https://picasaweb.go...itionerAug2012#
#2
Posted 06 August 2012 - 05:42 PM
You will need a volt meter to do the test.
Use the meter to verify 220volts at the incoming side of the contactor.
If voltage is good,press the center bar of the contactor by hand to see if the compressor and fan motor come on.
If they will come on,set the thermostat for COOL.
Then use the meter to check for 24 volts at the contactor solenoid terminals located on each side of the contactor.
If you have 24 volts here,replace the contactor.
If you do not have 24 volts here,re-set the pressure switch.
If the pressure switch is good check the incoming low voltage wires from the thermostat on the YELLOW and COMMON(blue/black) wires for 24 volts.
If no volts on YELLOW and COMMON either the thermostat is bad or you have a broken thermostat wire.
- Samurai Appliance Repair Man likes this
#3
Posted 06 August 2012 - 08:09 PM
model number ?... Replaced the capacitor (original was 40/3 but the store had only 40/5, which they said would work)
... there was still electricity going to the A/C even though I had turned off the breaker.
... Is it possible I shorted something or fried one of the electrical parts?
... Any good way to test what needs to be replaced?
... https://picasaweb.go...itionerAug2012#
1) 40/3 = 40 is for the Compressor ... 3 is for the Fan ... 5 is nearly 2x3 .. more important what voltage rating ?
2) something's wired wrong .. who knows ?
3) yes
4) .. won't know until the wiring is corrected
5) ... "Sorry, that page was not found."
- Samurai Appliance Repair Man likes this
one of my video productions: “Easter Seals: Walk With Me”
every day is Down Syndrome Awareness Day
"A Child Is Waiting" . Burt Lancaster . Judy Garland . 1962
RegUS_PatOff > www.youtube.com/watch?v=oPAY2LsKVEw
#4
Posted 07 August 2012 - 10:10 AM
RegUS - let me get some additional information for you as per your questions and get back to you.
#5
Posted 07 August 2012 - 06:46 PM
Also, here are two pictures of the label on the new capacitor, as installed. I brought the old one to the appliance store, showed it to the guy, and he said this one would work:
http://goo.gl/LrIUz
http://goo.gl/C9GBU
Can you confirm that everything is ok and then I can follow jumptrout's suggestions for troubleshooting (or let me know if you have other suggestions).
Thanks.
#6
Posted 08 August 2012 - 04:47 AM
One other thing - when I first went to replace the capacitor, for some reason, there was still electricity going to the A/C even though I had turned off the breaker. I managed to get some sparks before I realized this and turned off the main feed to the house. Is it possible I shorted something or fried one of the electrical parts? Any good way to test what needs to be replaced?
It's possible the capacitor was still holding a charge. You should have not only a circuit breaker but also a service disconnect at the condenser. Hopefully this unit was professionally installed by a reputable contractor.
- Samurai Appliance Repair Man likes this
#7
Posted 08 August 2012 - 05:57 AM
Trace your components for power both low and high voltage.
Look closely at the contact points on the contactor.
They may burned and deteriorated.
If everything works except the fan,replace the fan motor.
Get a motor rated for a 5 mfd cap.
Edited by jumptrout, 08 August 2012 - 05:58 AM.
- Samurai Appliance Repair Man likes this
#8
Posted 08 August 2012 - 09:37 AM
It's possible the capacitor was still holding a charge. You should have not only a circuit breaker but also a service disconnect at the condenser. Hopefully this unit was professionally installed by a reputable contractor.
Thanks - capacitor still holding charge is possible. How do I locate/identify the service disonnect?
Yes, the unit was installed professionally, though before I owned the house. The capacitor replacement was the only thing I've done to it other than clean it.
#9
Posted 08 August 2012 - 09:42 AM
Voltage rating on the cap is good.
Trace your components for power both low and high voltage.
Look closely at the contact points on the contactor.
They may burned and deteriorated.
If everything works except the fan,replace the fan motor.
Get a motor rated for a 5 mfd cap.
Thanks. Going to follow your prior instructions for testing voltage at contactor. Just to clarify - I can test the voltage at the screws on the top of the contactor, right? There is also a brown wire and a yellow wire running off the side of the contactor to the delay-on unit. Should I test those? What about the big black cylinder at the top with the red wires coming out?
#10
Posted 08 August 2012 - 01:59 PM
#11
Posted 08 August 2012 - 06:20 PM
FYI: the dirt your ac is setting on was created slightly before the ac itself was created. Maybe within a week or so.
Edited by Bullstok, 08 August 2012 - 08:08 PM.
#12
Posted 10 August 2012 - 08:23 AM
Pushed down the center bar of the contactor and the unit turned on (both compressor and fan). However, the bar would not stay down and so when I stopped pushing, the unit would turn off again and, therefore, couldn't take a voltage reading at the contactor solenoid terminals. I presume that I need to change out the contactor...correct? Anything else I should change out while I'm doing that?
#13
Posted 10 August 2012 - 04:57 PM
Set the thermostat for COOL and lower the temperatture on the stat.
Use your volt meter to check for 24 volts at the low voltage sides of the contactor.
If you have voltage the contactor is bad.
If you do not have voltage it could be the thermostat,the low voltage wiring or a low pressure switch in the condenser circuit.
If you have a wiring diagram,post a picture of it here.
- Samurai Appliance Repair Man likes this
#14
Posted 13 August 2012 - 08:37 PM
There should be a yellow wire coming in from the thermostat and going to the terminal strip. From there, either a yellow or a violet wire will continue to the anti-short cycle timer. Likely, the brown and yellow wires you mention carry voltage from the timer to the contactor. Check for 24 VAC across them when the thermostat is calling for cool.
But first, your service disconnect will be a gray metal junction box with a lid. It should be mounted right on the unit. It will have a thick gray cable leading into it (that's called the whip). Open that cover and you should see a pull-out connector or a heavy duty switch.
Edited by jb8103, 13 August 2012 - 08:40 PM.
#15
Posted 15 August 2012 - 09:15 PM
1. Found the service disconnect - thanks, very helpful to use that.
2. Switched out the contactor
3. Unit still not working, but I realized that my multimeter is not working either so I can't accurately diagnose right now.
4. Here is a picture of the circuit diagram that's on the inside panel: https://picasaweb.go...003130614315954 It pretty unclear so I drew a diagram by tracing the wires to the different devices: https://picasaweb.go...086934698155634
Will pick up a new multimeter tomorrow. I think I understand where to take the 24v measurements, but, not sure how to pinpoint the thermostat,the low voltage wiring, the low pressure switch in the condenser circuit (what is that?), or the anti-short cycle timer.
Thanks.
#16
Posted 15 August 2012 - 09:19 PM
#17
Posted 16 August 2012 - 06:59 AM
Post the wire colors and their letter designation.
Example: Red on R....Yellow on Y....Blue on C.......etc.
The Time Delay Relay is most likely the problem since you replaced the contactor and got no joy.
Once you provide the thermostat schematic I can instruct you on by-passing the time delay.
Do you have a digital thermostat?
- Samurai Appliance Repair Man likes this
#18
Posted 16 August 2012 - 04:42 PM
The blower does come on when the thermostat is set to COOL, so at a minimum the thermostat is sending a signal out to that device.
Here is a pic of the thermostat:
Edited by roomservicetaco, 16 August 2012 - 07:36 PM.
#19
Posted 17 August 2012 - 03:50 AM
The anti-short cycle timer is the "delay on break" circuit you have marked there. Same thing.
The low pressure switch is probably inside the hermetically sealed compressor. Not to worry.
What you have marked "freon valve(?)" is intriguing.
But anyway, the thermostat cable is likely a brown jacketed cable coming from the house and leading into the lower section of the electrical box in the unit. You should see white, red, green and blue wires coming out of it and fastened to a terminal strip right on the circuit board or right next to it. (Blue should be yellow.)
The blue sends power to the contactor through the delay on break component. Jumptrout will explain how to bypass that, which is almost certainly the problem child here.
#20
Posted 17 August 2012 - 04:16 AM
Edited by jb8103, 17 August 2012 - 04:20 AM.
0 user(s) are reading this topic
0 members, 0 guests, 0 anonymous users
FAQs | Parts | Memberships | Repair Videos | Newsletter | Beer Fund | Contact
Your Sometimes-Lucid Host:
"If I can't help you fix your appliance and make you 100% satisfied, I will come to your home and slice open my belly,
spilling my steaming entrails onto your floor."
ApplianceGuru.com | AppliancePartsResource.com | Fixitnow.com