Jump to content
Click here to check out our structured, online appliance repair training courses for rookies and experienced techs.

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 30 March 2024 02:00 PM Until 03:00 PM
      0  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This workshop is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      If you have a specific appliance problem you'd like us to talk about, post it here! We need a problem statement and a PDF of the tech sheet or schematic so we can all see it on screen share. If you have a PDF that isn't already in the File library here at Appliantology, send it to us by attaching it to the contact form. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, March 30 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Troubleshoot problem with Ruud A/C


roomservicetaco

Recommended Posts

roomservicetaco

I have a small home/office that is detached from my home and it has it's own A/C unit. Last Monday, I came into the office in the morning and the air handler was blowing air, but the A/C unit was not working, such that the A/C was blowing warm air.

Took the unit apart and got it to the point where the compressor was working but the fan was not spinning (I pressed the button labeled "High Pressure Control Release/Reset" though I'm not sure if pressing this button was what got the compressor turned on or not). Got the fan to spin manually, so figured the issue was just the capacitor.

Replaced the capacitor (original was 40/3 but the store had only 40/5, which they said would work) but now I can't get anything to turn on - either the compressor or the fan.

Is there a good way to troubleshoot what other parts may need to be replaced?

One other thing - when I first went to replace the capacitor, for some reason, there was still electricity going to the A/C even though I had turned off the breaker. I managed to get some sparks before I realized this and turned off the main feed to the house. Is it possible I shorted something or fried one of the electrical parts? Any good way to test what needs to be replaced?

Thanks.

Here are the relevant pictures (last one is of the unit with the replacement capacitor installed. It was smaller in diameter than the old one, so I needed to fill with some weather stripping.) The "reset" button is the red one at the bottom center of the first picture.

https://picasaweb.google.com/107780298508392297455/AirConditionerAug2012#

Link to comment
Share on other sites

  • Replies 23
  • Created
  • Last Reply

Top Posters In This Topic

  • roomservicetaco

    10

  • jumptrout

    7

  • jb8103

    4

  • RegUS_PatOff

    1

Your picture link does not work for me.

You will need a volt meter to do the test.

Use the meter to verify 220volts at the incoming side of the contactor.

If voltage is good,press the center bar of the contactor by hand to see if the compressor and fan motor come on.

If they will come on,set the thermostat for COOL.

Then use the meter to check for 24 volts at the contactor solenoid terminals located on each side of the contactor.

If you have 24 volts here,replace the contactor.

If you do not have 24 volts here,re-set the pressure switch.

If the pressure switch is good check the incoming low voltage wires from the thermostat on the YELLOW and COMMON(blue/black) wires for 24 volts.

If no volts on YELLOW and COMMON either the thermostat is bad or you have a broken thermostat wire.

Link to comment
Share on other sites

... Replaced the capacitor (original was 40/3 but the store had only 40/5, which they said would work)

... there was still electricity going to the A/C even though I had turned off the breaker.

... Is it possible I shorted something or fried one of the electrical parts?

... Any good way to test what needs to be replaced?

... https://picasaweb.go...itionerAug2012#

model number ?

1) 40/3 = 40 is for the Compressor ... 3 is for the Fan ... 5 is nearly 2x3 .. more important what voltage rating ?

2) something's wired wrong .. who knows ?

3) yes

4) .. won't know until the wiring is corrected

5) ... "Sorry, that page was not found."

Link to comment
Share on other sites

roomservicetaco

Model number: UAPA-024JAZ - see picture here for entire label: https://picasaweb.google.com/107780298508392297455/AirConditionerAug2012#5774080675971223330

Also, here are two pictures of the label on the new capacitor, as installed. I brought the old one to the appliance store, showed it to the guy, and he said this one would work:

http://goo.gl/LrIUz

http://goo.gl/C9GBU

Can you confirm that everything is ok and then I can follow jumptrout's suggestions for troubleshooting (or let me know if you have other suggestions).

Thanks.

Link to comment
Share on other sites

One other thing - when I first went to replace the capacitor, for some reason, there was still electricity going to the A/C even though I had turned off the breaker. I managed to get some sparks before I realized this and turned off the main feed to the house. Is it possible I shorted something or fried one of the electrical parts? Any good way to test what needs to be replaced?

It's possible the capacitor was still holding a charge. You should have not only a circuit breaker but also a service disconnect at the condenser. Hopefully this unit was professionally installed by a reputable contractor.

Link to comment
Share on other sites

Voltage rating on the cap is good.

Trace your components for power both low and high voltage.

Look closely at the contact points on the contactor.

They may burned and deteriorated.

If everything works except the fan,replace the fan motor.

Get a motor rated for a 5 mfd cap.

Edited by jumptrout
Link to comment
Share on other sites

roomservicetaco

It's possible the capacitor was still holding a charge. You should have not only a circuit breaker but also a service disconnect at the condenser. Hopefully this unit was professionally installed by a reputable contractor.

Thanks - capacitor still holding charge is possible. How do I locate/identify the service disonnect?

Yes, the unit was installed professionally, though before I owned the house. The capacitor replacement was the only thing I've done to it other than clean it.

Link to comment
Share on other sites

roomservicetaco

Voltage rating on the cap is good.

Trace your components for power both low and high voltage.

Look closely at the contact points on the contactor.

They may burned and deteriorated.

If everything works except the fan,replace the fan motor.

Get a motor rated for a 5 mfd cap.

Thanks. Going to follow your prior instructions for testing voltage at contactor. Just to clarify - I can test the voltage at the screws on the top of the contactor, right? There is also a brown wire and a yellow wire running off the side of the contactor to the delay-on unit. Should I test those? What about the big black cylinder at the top with the red wires coming out?

Link to comment
Share on other sites

Don't know what black cylinder/red wire you are referring to. Pictures are not coming up for me.

Link to comment
Share on other sites

The cylinder you mention is a start capacitor with a relay to cut it off. Note that it is different than the run capacitor you have been dealing with. It is sort of the equivalent of a hard start capacitor nowadays. It boosts the compressor to get it going.

FYI: the dirt your ac is setting on was created slightly before the ac itself was created. Maybe within a week or so.

Edited by Bullstok
Link to comment
Share on other sites

roomservicetaco

Thanks everyone.

Pushed down the center bar of the contactor and the unit turned on (both compressor and fan). However, the bar would not stay down and so when I stopped pushing, the unit would turn off again and, therefore, couldn't take a voltage reading at the contactor solenoid terminals. I presume that I need to change out the contactor...correct? Anything else I should change out while I'm doing that?

Link to comment
Share on other sites

Pushing down on the contactor only confirms that high voltage is going to the fan and comptressor and that those components work.

Set the thermostat for COOL and lower the temperatture on the stat.

Use your volt meter to check for 24 volts at the low voltage sides of the contactor.

If you have voltage the contactor is bad.

If you do not have voltage it could be the thermostat,the low voltage wiring or a low pressure switch in the condenser circuit.

If you have a wiring diagram,post a picture of it here.

Link to comment
Share on other sites

I had a similar situation recently. Control voltage to the contactor is controlled by the anti-short cycle timer, in my case that was a small circuit board. It was not passing voltage to the contactor. We can rule out the capacitors since the compressor and condenser fan start when the contactor is manually actuated.

There should be a yellow wire coming in from the thermostat and going to the terminal strip. From there, either a yellow or a violet wire will continue to the anti-short cycle timer. Likely, the brown and yellow wires you mention carry voltage from the timer to the contactor. Check for 24 VAC across them when the thermostat is calling for cool.

But first, your service disconnect will be a gray metal junction box with a lid. It should be mounted right on the unit. It will have a thick gray cable leading into it (that's called the whip). Open that cover and you should see a pull-out connector or a heavy duty switch.

Edited by jb8103
Link to comment
Share on other sites

roomservicetaco

Thanks for all the good information. A quick update:

1. Found the service disconnect - thanks, very helpful to use that.

2. Switched out the contactor

3. Unit still not working, but I realized that my multimeter is not working either so I can't accurately diagnose right now.

4. Here is a picture of the circuit diagram that's on the inside panel: https://picasaweb.google.com/107780298508392297455/AirConditionerAug2012#5777003130614315954 It pretty unclear so I drew a diagram by tracing the wires to the different devices: https://picasaweb.google.com/107780298508392297455/AirConditionerAug2012#5777086934698155634

Will pick up a new multimeter tomorrow. I think I understand where to take the 24v measurements, but, not sure how to pinpoint the thermostat,the low voltage wiring, the low pressure switch in the condenser circuit (what is that?), or the anti-short cycle timer.

Thanks.

Link to comment
Share on other sites

Remove the cover plate on the thermostat to view the wire connections.

Post the wire colors and their letter designation.

Example: Red on R....Yellow on Y....Blue on C.......etc.

The Time Delay Relay is most likely the problem since you replaced the contactor and got no joy.

Once you provide the thermostat schematic I can instruct you on by-passing the time delay.

Do you have a digital thermostat?

Link to comment
Share on other sites

roomservicetaco

Yes, digital thermostat. Looks like White on W, Red on RC and another red connecting RH and RC, then Green on G, and Blue(?) on Y. Picture below.

The blower does come on when the thermostat is set to COOL, so at a minimum the thermostat is sending a signal out to that device.

Here is a pic of the thermostat:

thermostat.JPG

Edited by roomservicetaco
Link to comment
Share on other sites

Blue on "Y" is the guy we're after. Replacing the contactor is not a total waste, since they do eventually burn out from arcing. A fresh one won't hurt a bit.

The anti-short cycle timer is the "delay on break" circuit you have marked there. Same thing.

The low pressure switch is probably inside the hermetically sealed compressor. Not to worry.

What you have marked "freon valve(?)" is intriguing.

But anyway, the thermostat cable is likely a brown jacketed cable coming from the house and leading into the lower section of the electrical box in the unit. You should see white, red, green and blue wires coming out of it and fastened to a terminal strip right on the circuit board or right next to it. (Blue should be yellow.)

The blue sends power to the contactor through the delay on break component. Jumptrout will explain how to bypass that, which is almost certainly the problem child here.

Link to comment
Share on other sites

Just FYI.The engineers prefer that we consumers do not stop and start the compressor more often than once every three minutes. This can happen when we fiddle with the thermostat, so a timer is built in to prevent a re-start.A digital thermostat also has a timer built in, which is why Jumptrout asked if you had a digital. Now he knows he can safely bypass the timer in the condensing unit, at least temporarily. Providing we see control voltage going in to the timer, but no control voltage at the contactor when the thermostat is calling for cool. Your problem should be solved after you follow his instructions.

Edited by jb8103
Link to comment
Share on other sites

Turn off power to the air handler.

Turn off power to the condenser.

Remove the 2 BROWN wires from the delay on break relay.

Join them together with a wire nut.

This will send the COMMON from the transformer directly to the contactor.

Do the same with the 2 YELLOW wires on the delay on break relay.

This sends YELLOW(low voltage line) to the contactor.

Turn power on at air handler and condenser.

Set the thermostat to COOL.

Wait up to 5 minutes for the thermostat to reset and send power to the contactor.

Use your volt meter set for AC volts to check for 24 volts at the contactor BROWN and YELLOW wires.

If this works you can leave the delay relay out of the circuit because the digital stat will provide the time delay.

Link to comment
Share on other sites

roomservicetaco

Thanks. Yes, the wire coming from the house/thermostat is brown (bottom left of my drawing). It breaks into a red and a black wire, where the red goes to the Delay On Break and the black goes to the "freon valve." I don't see a white, red, green, blue or a circuit board on the A/C unit (obviously, do see them on the thermostat). Will take a picture and and post it.

What I labeled "freon valve" may not be a valve at all. It is 2 yellow wires going into a junction on a copper tube where, I assume, freon flows. Will take a pic of that as well.

Would it just be worth swapping out the "delay on break" / short circuit timer or should I wait to test it by bypassing it first?

Link to comment
Share on other sites

Turn off power to the air handler.

Turn off power to the condenser.

Remove the 2 BROWN wires from the delay on break relay.

Join them together with a wire nut.

This will send the COMMON from the transformer directly to the contactor.

Do the same with the 2 YELLOW wires on the delay on break relay.

This sends YELLOW(low voltage line) to the contactor.

Turn power on at air handler and condenser.

Set the thermostat to COOL.

Wait up to 5 minutes for the thermostat to reset and send power to the contactor.

Use your volt meter set for AC volts to check for 24 volts at the contactor BROWN and YELLOW wires.

If this works you can leave the delay relay out of the circuit because the digital stat will provide the time delay.

Do this.

The delay on break is not necessary with a digital thermostat.

Link to comment
Share on other sites

  • 3 months later...

For one that's a heat pump. That "valve" must be the reversing valve. You have low and high pressure switches. The HP switch has a reset button next to the suction line connection on the back of the unit. There's a red rubber button sticking out. Push in on it and see if it makes a click. Your LP switch should only be out if you lost most of your freon. Pretty easy to depress the pressure port strader valve to make sure you still have good pressure. If either switch is open no 24v signal reaches the contactor. I agree; bypass the delay timer.