Samurai on Facebook - become a fan today! Sign up for our free newsletter and keep up with all things Appliantology. Subscribe to our YouTube channel for lots of appliance repair tips and help! Follow the Samurai on Twitter and get timely morsels of Appliantological Wisdom! Subscribe to our MST Radio podcast to learn secrets of the trade.
torchkeeper

a/c leaking at sweat fitting on outside of a-coil

11 posts in this topic

a/c guy did lousy job sweating low pressure line to fitting into a-coil. wondered why he restarted vacumm pump a second time ! OIL and can see a small bubbling pin hole oil comming out. So am I going to lose the charge. Can I pull charge back into condenser and resweat fitting ? buubling as we speak ,what do I do now?

Thanks for the help

Share this post


Link to post
Share on other sites

Need appliance parts? Call 877-803-7957 now!

you can pump the refrigerant into condenser coil usually and recover any refrigerant,then try to braze fitting- However, make sure youre not voiding your warranty,if any, by doing so. I would contact that a/c co. to have them repair.

Share this post


Link to post
Share on other sites

No warranty ,built new house on different location on same property , moved a/c and tappan / nordyne furnace to new home. Had to get a tech to do charging on his own. None of local hvac companies wanted to install my equipment. Furnace only had a couple hundred hours and a/c same. I understand their concern with used units though. Had to install all runs , trunckline ,returns ect. Was refered to guy , he had a couple moments of competence ! Sweat joint look like welding splatter, this unit has the orifices right on a-coil and line set sweated to orifices. Run me through parking refrigerant in condenser. I have a new set of gauges and a new vacumm pump if Ineed it. if i can save it ,I will resweat bad lineset connerction.

Share this post


Link to post
Share on other sites

Just now seeing this. Yes,you will have to vacuum the system after your repair before you release the refrigerant back inside.

Share this post


Link to post
Share on other sites

So, are you asking how to recover the refrigerant back into the condenser? Easy...just close off the pressure valve at the condenser unit and run for 20 minutes or so. then shut off the pressure high side valve thus pulling the refrigerant back into the compressor.LG has a pretty good tutorial in their mini split literature as I recall. .Not sure where you would find it, but it is open format and available on the web iI'm pretty sure good luck.

Share this post


Link to post
Share on other sites

PS...be sure to triple evacuate the lineset before you open the valves and return the system to service. Some might reccomend trickling nitrogen through the system as you braze the joint to reduce oxidation in the line. Saw a pretty cool youtube video not long ago on this.

Share this post


Link to post
Share on other sites

"run for 20 minutes or so" WRONG !!! BIG TIME WRONG !! after this you can replace the compressor . if you run a scroll compressor in a vacuum you will ruin it in just a few seconds . if it's a hermetic it will over heat in 5 mins or less

correct way , even though i never like to do this , sometimes the condenser cannot hold all the freon in the system and i have seen compressors ruined this way ! so be careful !

run system

connect your manafold set

close high side service valve , pressure will not drop for 60 seconds or so and then it drops quick ! , when you get down to right above zero pull disconect .

close low pressure service valve

vent anything left in lines to the air through manafold set

leave manafold set open(to air) when brazing

pull a vacuum on system with pump

turn off manafold set and pump and wait for an hour or so and look for rise in low pressure gauge

if no . turn on service valves and let freon back in , replace disconect and start unit

Share this post


Link to post
Share on other sites

thanks bob. I stand corrected.It was late and I was working off of memory.Didnt realize it came down so fast.Are Inverter mini splits any different?This is oil country AC is just coming into fashion up here in the Maine woods, like flush toilets.

Share this post


Link to post
Share on other sites

Thank you all, one last question. When service valves are closed what does manifold gauges read? Pressure to lineset side or compressor side? I am thinking lineset side or how else would I read vacumm in lineset. Right ro wrong ?

Share this post


Link to post
Share on other sites

you are just reading the lineset and A coil, I think. Ill defer to greater minds on this....

Share this post


Link to post
Share on other sites

You will be reading the lineset and Evaporator coli.

Share this post


Link to post
Share on other sites