Jump to content
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 27 April 2024 02:00 PM Until 03:00 PM
      5  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological. 
      We have a special session planned for this one. Instead of the usual Show 'n Tell on a technical topic, we're going to post tech sheets in the comments to this Calendar Event (scroll down to see what's posted so far) and ask specific questions that can only be answered by reading the tech sheet. If you at least try to answer the questions beforehand, you'll get a lot more out of it. The tech sheet and the questions are posted in the comments section below.
      Your mission, if you should choose to accept it, is to check out the questions for each one and try to answer them ahead of time. Then come to the Dojo to see how well you did! 
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, April 27 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Heat Pump Not Cooling


ApplianceDoctor

Recommended Posts

I have a customer called and said that their heat pump was not cooling. When I arrived I confirmed that there was a problem and unit was not cooling. I found everything was running even the compressor was running. I connected gauges to unit and found while compressor was running the high and low side pressures were equalized. This sounds to me like a bad or inefficient compressor. Is there any other thing or component could be bad in this unit that would cause the high and low pressure to be equalized while the compressor is running? Can anyone help me with this?

 

Thank You

 

ApplianceDoctor

Link to comment
Share on other sites

What refrigerant is in system?

What are the pressures?
What are LRA draw? (locked rotor)

What is LRA rating?
What are running amp draw?

What is running amp rating?

Is reversing valve actuating or stuck mid range?

Link to comment
Share on other sites

Refrigerant is R-22

Low side pressure 125 psig

High side pressure 125 or 130

LRA rating on compressor 48 amps

Unit is actually drawing while running 3.7 amps

Info. on label on unit is wore off could not see RLA

I can hear reversing valve clicking and energizing but

cant hear sound of gas switch.

Pressures are equalized or almost equalized.

Link to comment
Share on other sites

I don't work on a lot of a/c heat pumps, no heat in south florida, but it sounds like your reversing valve is stuck mid position. try hitting it with the back of a screwdriver and try putting on the heat see if it moves and what are the pressures in heat?

Ahh-Cool A/C

Link to comment
Share on other sites

Running amps is too low.

Remove the compressor relay cover and check for a broken wire on compressor.

Verify the compressor capacitor is good.

  • Like 1
Link to comment
Share on other sites

How would the compressor be running with a broken wire? Even if it had a bad capacitor, would the compressor still run as it is doing? I have run unit in heat and cool position and pressures are still equalized. Would a reversing valve stuck in mid position cause the pressures to be equalized?

 

Thanks

 

ApplianceDoctor

Link to comment
Share on other sites

again I don't work on a lot of heat pumps. the compressor pumps refrigerant to the reversing valve and the valve determins which way the refrigerant goes. if it's stuck in mid position it willpump to the valve and bypass right back to the compressor

Link to comment
Share on other sites

Thanks guys for all your help.

 

ApplianceDoctor

Link to comment
Share on other sites

Sounds like he's given up on us.

 

I don't believe the compressor is running. He's hearing a lot of racket from the outside unit fan, and assuming the compressor is making some of that racket.

 

Where in the circuit did he check for amp draw? Did he mistakenly get the fan L1? 3.7 A would be about right.

 

It is not likely that pressures would be equal on both sides if the compressor was actually running. 125 PSIG corresponds to about 100 degrees F ambient, typical of an outdoor coil in the summer sun. The indoor coil P/T would correspond if he's taking pressures at the outdoor coil.

 

I'd have to be standing there to say for sure, but I bet our man has a bad capacitor.

Edited by jb8103
Link to comment
Share on other sites

the fan amp draw should be anywhere between .8 and 1.5. 3.7 is too much for a fan, unless the fan is bad

Link to comment
Share on other sites