Jump to content
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 30 March 2024 02:00 PM Until 03:00 PM
      0  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This workshop is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      If you have a specific appliance problem you'd like us to talk about, post it here! We need a problem statement and a PDF of the tech sheet or schematic so we can all see it on screen share. If you have a PDF that isn't already in the File library here at Appliantology, send it to us by attaching it to the contact form. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, March 30 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Reversing Valve


ApplianceDoctor

Recommended Posts

How can you tell if a reversing valve on a heat pump is stuck in mid position allowing gas to bypass from discharge side to suction side causing pressures to equalize?

 

Thank You

 

ApplianceDoctor

Link to comment
Share on other sites

If you believe the RV is stuck...set the system for COOL and run it.

While running...make and break the orange t-stat wire several times.(at the condenser)

You should hear the RV click.

Doing this several times can often unstick a stuck valve.-+

Watch your pressures as you do this.

If you see achange in pressure you know the valve has activated.

Link to comment
Share on other sites

I have found that the reversing valve is energized on the cooling cycle, but also even if thermostat is set to off position valve is still energized. If I cut breaker of to unit you can hear valve coil click as it is de-energizing, or if you put unit in heating cycle you can hear valve click as it is de-energizing. I have tried switching from heat to cool several times and it doesn't seem to make a difference. How can you tell for sure if valve is stuck in mid position or the compressor is inefficient?

Link to comment
Share on other sites

You are correct.

The valve is energized in the COOL setting.

What I described above will open and close the solenoid to possibly break loose a stuck valve.

Overall,your description is a bad compressor,running and not pumping.

Link to comment
Share on other sites

I tapped reversing valve with hammer and valve switched and started working correctly. Thanks for all your help.

 

ApplianceDoctor

Link to comment
Share on other sites

 I have tried switching from heat to cool several times and it doesn't seem to make a difference.

Just by the way, you were likely up against an anti-short-cycling device. The system, if so equipped, will ignore any change of setting made within two minutes of a previous change of setting.

Edited by jb8103
Link to comment
Share on other sites

  • 2 weeks later...

It sounds like you got it running and that's great but from my experience if it happened once it will happen again. The reversing valve should not get stuck in the middle of the valve during normal operation. This is one of the leading causes of compressor failure on heatpumps. If the compressor was damaged while the system was running with the reversing valve stuck in the middle of the valve make sure that a new reversing valve is installed with the new compressor.

  • Like 1
Link to comment