KitchenAid Refrigerator intermittent no cool

15 posts in this topic

KSRS27ILBT03

 

I checked this one out about a week a go.  It was cooling fine that day, but customer just called and said the freezer up to 40 degrees.  She stated that sometimes it will begin to cool again after she un-plugs it for a few minutes.

 

Evap fan is operating in the no cool state.

 

I'm thinking control board 8201658

 

Anyone else run across one of these?

Share this post


Link to post
Share on other sites

Need appliance parts? Call 877-803-7957 now!

Had similar issue with a built-in that had both Gemini and niagra boards.  Intermittent temp problems.  Couldn't pin it down.  Tech-line advise replacing both controls.  Still had temp issues.  Finally replaced interface control board and that fixed it.  Have you tried accessing diagnostic mode for component checks?

Share this post


Link to post
Share on other sites

Thanks Pduff and Samurai for the replies.  I did go through the diagnostics but it was pointless as the refer was cooling at that time.  I'm going back out tomorrow to take a look at it, and hopefully it will still be in a broken state.

 

By looking at the parts breakdown, the only control I can see is the aforementioned board that the Samurai has supplied a link to.  There is a thermistor that  could be replaced as well (2188819).

 

If this thing had analog controls I'd already have a cold control on order and call it a day.

 

The stakes go up quite a bit between a $60 cold control and $200 control board.

 

Thanks again for the assistance.

Share this post


Link to post
Share on other sites

Affirmative on the control.  As far as the true nature of the problem within the control I can only guess it was defrost related by the conditions noticed.  Sometimes found frost and overcooling in frz section and sometimes warmer temps like 40 degrees and lots of moisture in freezer.  Sound familiar?

Share this post


Link to post
Share on other sites

KSRS27ILBT03

Evap fan is operating in the no cool state.

Re-read your post. Are you saying here that the evap fan is running when the compressor is not? If so, you may have a flakey compressor relay or a loose connection at the relay. Been bitten by that one before. Check it out.

Share this post


Link to post
Share on other sites

Re-read your post. Are you saying here that the evap fan is running when the compressor is not? If so, you may have a flakey compressor relay or a loose connection at the relay. Been bitten by that one before. Check it out.

 

Great point!  I will give it a thorough examination.  Thanks for the tip!

Share this post


Link to post
Share on other sites

Update:  So I arrive today to investigate the KA refer that only cools when it wants to.  Of course, she is back to down to zero in the freezer and everything is running as advertised.

 

With the voice of the Samurai still echoing in my head, I pull the refer from it's crevice and take the back panel off.  Being a previous in-warranty type of guy (Maytag compressor start relay recall survivor) this is a familiar sight.  I pull the compressor start device off, shake shake, rattle rattle - BINGO!

 

Thanks again to the Samurai & PDuff for the assistance.

 

I have replaced many compressor start devices, but have not until today, seen it cause such intermittent cooling issues.  One day older, one day wiser.

Share this post


Link to post
Share on other sites

Right there with ya, Thirstytech.  I try to catch the simple solutions when I can but still tend to yell Yeehah and jump right to the big stuff.  Sure did love all those free replay kits from the Maytag/Whirlpool reworks.  What kind of relay did you mind on this one?  Big, square white Klixon style?  Must've been on the verge of full on failure.

Share this post


Link to post
Share on other sites

Nice job! Ran into a similar problem recently, that how I knew to point it out. Here's the story:

Share this post


Link to post
Share on other sites

Right there with ya, Thirstytech.  I try to catch the simple solutions when I can but still tend to yell Yeehah and jump right to the big stuff.  Sure did love all those free replay kits from the Maytag/Whirlpool reworks.  What kind of relay did you mind on this one?  Big, square white Klixon style?  Must've been on the verge of full on failure.

 

Yes sir, big square white one.  

Share this post


Link to post
Share on other sites

Nice job! Ran into a similar problem recently, that how I knew to point it out. Here's the story:

 

This Thursday afternoon... got a call... same WP SxS... the way the customer described, it was going to be a slam dunk start relay replacement... shake rattle and roll... compressor starts right up after installing the new relay.... and runs for about 30 seconds, then stopped running....  15 min, 1 part job turns into  45 mins with the ADC being the 2nt part...   it is rare to see two parts fail... but, just common enough, to make a YouTube Star!!

Share this post


Link to post
Share on other sites

put data logger in