From one extreme to another


  • Please log in to reply
30 replies to this topic

#21 bigbuck

bigbuck

    Sōhei

  • Appliantologist
  • PipPipPip
  • 236 posts
  • Location: USA
  • Flavorite Brew:Red Wine

Posted 05 July 2013 - 03:01 PM

You should not see icicles .Are the door gaskets closing ok?



Use the Appliantology Parts Search Box to Find What You Need!
Enter your model number, part number, type of appliance, brand, or even a part description.
365-day return policy on all parts purchased here, even electrical parts that have been installed!

#22 MaryW13

MaryW13

    Samanera

  • Grasshoppah
  • Pip
  • 13 posts
  • Location: USA
  • Flavorite Brew:Sam Adams

Posted 05 July 2013 - 03:01 PM

not long at all.  i unplugged it and took off the panel pretty quickly.  



#23 MaryW13

MaryW13

    Samanera

  • Grasshoppah
  • Pip
  • 13 posts
  • Location: USA
  • Flavorite Brew:Sam Adams

Posted 05 July 2013 - 03:06 PM

i believe they seal but i did notice that I don't need to pull with very much effort to open both the freezer and the fridge.  I did wipe them down yesterday in case they was something in the gaskets. They were clean.



#24 bigbuck

bigbuck

    Sōhei

  • Appliantologist
  • PipPipPip
  • 236 posts
  • Location: USA
  • Flavorite Brew:Red Wine

Posted 05 July 2013 - 03:07 PM

You should see frost from top to bottom.Maybe put back together and give it a day and then take apart again to look at frost pattern.



#25 Spannerwrench

Spannerwrench

    Senpai

  • Master Appliantologist
  • PipPipPipPip
  • 734 posts
  • Location: USA
  • Flavorite Brew:Maxwell House > Black Crown > Crown Royal with Ginger Ale

Posted 05 July 2013 - 03:17 PM



everything is running even at the lowest setting until i turn it to the off position.

The evaporator fan should cycle off when the compressor and condenser fan motor cycle off. If not the evaporator fan will continue to circulate air into the fresh food section, the freezer section would therefore warm up, but the thermostat would not cycle the cooling back on because the thermostat is satisfied until the freezer runs out of cold air. It's plug n play SOS I don't know how it could be wired wrong, but nothing surprises me anymore.
Also what was the part number of the fan motor used in the first repair?

"Suds are not good"
"They write directions for a reason"
"Make sure you're using it right before you say it's not working correctly"
"If if has a Diagnostic Test Cycle, Run it before and after you fix it!"
"Doing the same thing over and over again and expecting different results is insane"
"For every complex problem there is an answer that is clear, simple, and wrong."

"Occam's RAZOR 'the simplest answer is most often correct'"


#26 MaryW13

MaryW13

    Samanera

  • Grasshoppah
  • Pip
  • 13 posts
  • Location: USA
  • Flavorite Brew:Sam Adams

Posted 05 July 2013 - 03:18 PM

ok i will do that. I just want to say thank you all so much for your help.  Its nice to be able to interact with problem solving.  I know this must be difficult when you can't see the appliance in person.  This is an awesome website.  I"ll take a very accurate picture of the frost pattern tomorrow.



#27 MaryW13

MaryW13

    Samanera

  • Grasshoppah
  • Pip
  • 13 posts
  • Location: USA
  • Flavorite Brew:Sam Adams

Posted 05 July 2013 - 03:22 PM

The evaporator fan should cycle off when the compressor and condenser fan motor cycle off. If not the evaporator fan will continue to circulate air into the fresh food section, the freezer section would therefore warm up, but the thermostat would not cycle the cooling back on because the thermostat is satisfied until the freezer runs out of cold air. It's plug n play SOS I don't know how it could be wired wrong, but nothing surprises me anymore.
Also what was the part number of the fan motor used in the first repair?

I'm not sure because the service guy bought it.  



#28 bigbuck

bigbuck

    Sōhei

  • Appliantologist
  • PipPipPip
  • 236 posts
  • Location: USA
  • Flavorite Brew:Red Wine

Posted 05 July 2013 - 05:44 PM

The correct fan motor part Number is W10188389.I don't see how he could wire it wrong.I could see him putting in any fan motor that he had to get it to run.Most people would not stock that fan motor and would have to come back another day.Did he have to come back or did he have the fan motor on his truck?



#29 DurhamAppliance

DurhamAppliance

    Sho' Nuff Chozin

  • Grand Master Funk
  • 5,073 posts
  • Location: USA
  • Flavorite Brew:Bells Two Hearted

Posted 05 July 2013 - 06:15 PM

Sounds like the fan motor installed is moving air in reverse direction. check air flow direction in manual and compare.

I've seen maintenance guys put in whatever fan or fan blade they have resulting in air pouring into fridge through the return ports. Amazingly, the cold control did not regulate it. I posted a few months back a scenario where I was called out to fix a fridge for being too cold... top mount fridge.. no thermistors.. easy fix, or so I thought.

Maintenance had put in a fan weeks before they called me but failed to tell me. No damper motor so only thing I though it could be was cold control. Never asked or thought about incorrect parts being installed. I changed out cold control but got a call back two weeks later. That's when I noticed forceful air entering fridge through return ports.

Checked air direction and came here to ask what the correct airflow should be. Sensei Reg provided the manual and I found the fan was reversing the air. Landlord admitted he had someone else working on it. Put correct fan in and all is well. I still don't understand why the cold control did not turn the fan off when the temps were in the 20's. Hope this helps.

Durham Appliance Thrift & Repair, LLC

www.DurhamApplianceThrift.com


#30 bigbuck

bigbuck

    Sōhei

  • Appliantologist
  • PipPipPip
  • 236 posts
  • Location: USA
  • Flavorite Brew:Red Wine

Posted 05 July 2013 - 06:20 PM

Thats what i think to.



#31 bigbuck

bigbuck

    Sōhei

  • Appliantologist
  • PipPipPip
  • 236 posts
  • Location: USA
  • Flavorite Brew:Red Wine

Posted 05 July 2013 - 10:34 PM

The correct fan motor will turn the correct fan blade counter clock wise.






0 user(s) are reading this topic

0 members, 0 guests, 0 anonymous users


FAQs | Store | Memberships | Repair Videos | Academy | Newsletter | Beer Fund | Contact


Use the Appliantology Parts Finder to Get What You Need!
Enter a model number, part number, type of appliance, brand, or even a part description.
365-day return policy on all parts purchased here, even electrical parts that have been installed!

Your Sometimes-Lucid Host:
Samurai Appliance Repair Man
"If I can't help you fix your appliance and make you 100% satisfied, I will come to your home and slice open my belly,
spilling my steaming entrails onto your floor."


The Appliance Guru | Master Samurai Tech

Real Time Analytics