creating water chiller
#1
Posted 01 March 2006 - 05:23 PM
http://www.marinedep...ne.asp?ast==
ive planed on using a 1/2" x 36" titanium tube for the evaporator. water flow over evaporator/heat exchanger will be apx 500 gph
problems frig runs off cap tube. evaporator is not sized to compressor. will plugging occur due to major conduction from cooling water in direct contact? if evaporator is two small is superheat a large problem? or am i worried over nothing? frig is fairly new and runs off 134a. btu rating is apx 5600 or 1/2 hp
most grateful and humble
doug
#2
Posted 01 March 2006 - 07:36 PM
#3
Posted 02 March 2006 - 03:59 AM
the average water temperature will be apx 88 degrees f. the required temp is 82 degrees f. the total ammont of water is 220 gal.
where did you get your figures? is there some type of table?
#4
Posted 02 March 2006 - 10:44 AM
#5
Posted 02 March 2006 - 01:11 PM
dont know if the samurai can help in his pod cast he says he cant remember btu per s/f in room air conditioning, lol.
i never thought of using a formula like that. confuse my self with all those bizzar mollier charts.

the evaporator size would certainly play into it.
mostly i am concerned with plugging or superheating.
if you could, please explain to me plugging or superheating
#6
Posted 02 March 2006 - 04:52 PM
#7
Posted 02 March 2006 - 06:07 PM
I dont think that i have a problem other than efficieny.
my biggest problem would be trying to get a larger ti tube at a reasonable cost.
thanks for the help ex sears guy.
though i would love to try and figure out the actual temp take down.
if you could find anything and post it, it would be greatly appreciated!
thanks again
doug
#8
Posted 02 March 2006 - 06:15 PM
#9
Posted 03 March 2006 - 04:45 AM
again i suck when it comes to refrigeration. so i will post a drawing.
maybe you can look at it and tell me what you think.
#10
Posted 03 March 2006 - 07:48 AM
Let me see if I remember superheat. I believe that is the amount of heat that the evaporated refrigerant picks up after all the liquid is gone.
That's right, it's represented by the region to the right of the Mollier curve. If the evaporator is sized too small, the risk is that you won't evaporate all the refrigerant and you'll slam in the compressor with liquid refrigerant; this is called "slugging."
An over-size evaporator will evaporate the refrigerant too soon and you'll end with the evaporator mostly filled with superheated vapor, which has zero or even a negative refrigeration effect.
You can calculate the heat transfer from the evaporator in both the forced air and water chilling applications. But I'll be damned if I remember how to do that, that was waaaay back in my undergrad heat transfer class, musta been 1982. I still have all my notes and text books, so if you're really interested in pursuing this, Doug, I'll be glad to blow the dust off of 'em and see what I can remember.
"Plugging," as I've learned about it, is a problem where moisture gets in teh system, or is allowed in through sloppy service practices, and creates a cyclic ice plug at the point in the evaporator where the capillary tube enters it.
FAQs | Parts | Memberships | Consultations | Repair Videos | Newsletter | Beer Fund | Contact
#11
Posted 03 March 2006 - 11:12 AM
so an undersized evaporator causes slugging.
not the fact that the evaporator is submerged in water?
#12
Posted 03 March 2006 - 11:28 AM
#13
Posted 03 March 2006 - 11:44 AM
Water, air, the refrigerant and evaporator don't care about the medium, just the heat transfer rate. Heat will transfer between the evaporator and outside medium more efficiently in water that in air because the heat transfer coefficient is higher in water than air due to much lower boundary layer resistance. This means that the same evaporator used in air and then submerged in running water (assuming ambient temps are comparable) will experience a sudden increase in heat transfer rate and refrigerant will boil off sooner in the evaporator when submerged in running water. Slugging would not be a problem here; instead the problem would be excessive superheat.so sorry meant slugging.
so an undersized evaporator causes slugging.
not the fact that the evaporator is submerged in water?
If the evaporator were too small, from a heat transfer point of view, that would mean that the refrigerant wasn't exposed to the heat source long enough to completely boil off all the refrigerant. Since, in a capillary tube system, the next stop is the compressor, you're looking at refrigerant still in the liquid state slamming into the compressor at its suction port. This will fry a hermetic compressor in a heartbeat. In larger, industrial refrigeration systems, you'll often see an accumulator between the compressor and the evaporator just for this purpose because those big screw compressors (vs. the reciprocating piston compressors used in home refrigeration and air conditioning) can cost thousands of dollars to replace.
FAQs | Parts | Memberships | Consultations | Repair Videos | Newsletter | Beer Fund | Contact
#14
Posted 03 March 2006 - 11:52 AM
#15
Posted 03 March 2006 - 12:31 PM
#16
Posted 03 March 2006 - 12:32 PM
could i run two evaporators parallel. splitting the high pressure into two cap tubes. and the low back into one.
#17
Posted 03 March 2006 - 01:03 PM
#18
Posted 03 March 2006 - 03:31 PM
#19
Posted 03 March 2006 - 03:35 PM
is that easily done?
#20
Posted 03 March 2006 - 04:40 PM
0 user(s) are reading this topic
0 members, 0 guests, 0 anonymous users
FAQs | Parts | Memberships | Repair Videos | Newsletter | Beer Fund | Contact
Your Sometimes-Lucid Host:
"If I can't help you fix your appliance and make you 100% satisfied, I will come to your home and slice open my belly,
spilling my steaming entrails onto your floor."
ApplianceGuru.com | AppliancePartsResource.com | Fixitnow.com