Jump to content
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 27 April 2024 02:00 PM Until 03:00 PM
      5  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological. 
      We have a special session planned for this one. Instead of the usual Show 'n Tell on a technical topic, we're going to post tech sheets in the comments to this Calendar Event (scroll down to see what's posted so far) and ask specific questions that can only be answered by reading the tech sheet. If you at least try to answer the questions beforehand, you'll get a lot more out of it. The tech sheet and the questions are posted in the comments section below.
      Your mission, if you should choose to accept it, is to check out the questions for each one and try to answer them ahead of time. Then come to the Dojo to see how well you did! 
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, April 27 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Mismatch between condenser and evaporator


dbiberdorf

Recommended Posts

I've got a newish house (built in 2005). I had a home inspection done as I approach the end of my bumper-to-bumper warranty. One question the inspector raised, in light of my general dissatisfaction with the a/c system in my house, is the mismatch between condenser and evaporator. The condenser is rated 3.5 tons, evaporator at 5 tons. Both are made by Goodman Manufacturing.

In researching all of this, I've found precious little in the way of hard data on what such a mismatch really implies for the system. I'm currently pressing the a/c contractor (by way of the builder) to show me that Goodman supports and recommends this configuration. In the meantime, I'd like to learn from the great minds here what the real implications of this setup are.

Any insight is appreciated.

Link to comment
Share on other sites

  • Replies 4
  • Created
  • Last Reply

Yes, I've seen a similar combination before. It was a 13 SEER 3.5 ton condensing unit and the inside coil was a 5-ton 10 SEER unit. Ends up that is what Goodman spec'd for this condenser, didn't even need to change the piston in the coil.

Link to comment
Share on other sites

I have a Ultra High Efficiency Tempstar system and they match a 2.5 ton condensor with a 3.5 ton evaporator.  I guess it raises the SEER rating.  Mine is a seer 14 system.

Link to comment
Share on other sites

:dude: Your mismatch is bad news.

Sometimes the air handler is upsized by 1/2 ton to boost airflow in a system with alot of duct transitions, etc. Your system is limited to the condenser capacity. In other words the evaporator can try to remove 5 tons, but the condenser can only unload 3.5 tons. The rest results in higher pressures and a warmer evaporator coil.

If you can get the builder to straighten it out, you should have him do so.

Link to comment