Jump to content
LIMITED TIME OFFER: Use code 10YEARS10 to get 10% off your Appliantology membership. Click here for more ×
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 27 April 2024 02:00 PM Until 03:00 PM
      0  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This workshop is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      If you have a specific appliance problem you'd like us to talk about, post it here! We need a problem statement and a PDF of the tech sheet or schematic so we can all see it on screen share. If you have a PDF that isn't already in the File library here at Appliantology, send it to us by attaching it to the contact form. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, April 27 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Payne furnace 396GAW048125


fixadryer

Recommended Posts

happy thanksgiving! (of course)

18 year old Payne furnace has worked fine all these years.  All of a sudden - blowing cold, burners won't stay lit more than 4 seconds.  I have bought new and replaced the control board (ie ICM271C).  I have bought new and replaced the spark igniter (ie Carrier LH680512).  I have shorted LIM1 and LIM2. I have confirmed ground to the chasis.  I have replaced the batteries in the Honeywell thermostat.

Immediately after replacing the spark igniter, the burners came on for about a minute, but after that, we're back to 4 seconds, although the igniter now retains its red glow constantly when the thermostat is calling for heat.  Sometimes, it's 25 seconds blower with no flame, and 4 second blower with flame.  Other times, the blower shuts off, and flame on for four seconds.  Unfortunately, the house isn't heating up above 58 degrees. 

Any thoughts???

Link to comment
Share on other sites

  • Replies 3
  • Created
  • Last Reply

If your unit has a combustion fan motor, use a manomenter to see that you are getting the correct pressures during pre purge and after ignition  to keep the proving switch closed. 

While you have the manometer out, check your inlet and outlet pressures to the gas valve while it is  trying to run.  I would use a jumper and send 24 VAC  straight to the gas valve  while the ignitor is glowing and force the valve to stay open  so that I can check the  pressures  on both halves of the gas valve while running.  This will prove that the valve itself is good also.  You may see that  you are not getting your 3.5 inches of WC (assuming you are using natural gas) for very long after ignition on the mainfold side.  You may see the higher pressure on the inlet side of the valve not staying at about 5 inches or more to provide adequate gas pressure and volume to the valve.

Bleed the gas line one good time and remove any and all air that will have accumulated.  That will give you a chance to see if your gas regulating valve is opening (provided you have one).

Be sure to check the obvious before you start all of this....make sure the gas meter is not pinned and is on.  You would not believe how many people I have to give a $100 service ticket to after going out on their no heat calls only to tell them the meter is off.  The residual gas left in the lines is enough to cause the same type of problems you are seeing.

These are most of the mechanical things I would check.  The only remaining things I would look for is along the 24 VAC lines.  Make sure you are getting at least 24 VAC and that you are not bleeding voltage off somewhere due to defective connections, wiring, or improper VA rating on the transformer.

1*

Link to comment
Share on other sites

  • 2 weeks later...

ok, well, I thought I'd circle back and let everyone know what it was, as I called a service tech in, who checked the inductance around the wires during the various light sequences

he replaced what he called the "ignition key", although, it looks to me like it's the main gas valve, he said the solinoid had gone bad after 18 years of cycling on and off, his repair fixed my initial problem

but created a new problem, BOOM! :yikes: when the furnace came on with the burners cold, sometimes a yellow flame extending out several inches from the furnace - not good

I then had the furnace serviced, which it hasn't been done in the 13 years I've owned the house, and after all the rust and debris was cleaned out of the burners, the furnace now works beautifully :)