Samurai on Facebook - become a fan today! Sign up for our free newsletter and keep up with all things Appliantology. Subscribe to our YouTube channel for lots of appliance repair tips and help! Follow the Samurai on Twitter and get timely morsels of Appliantological Wisdom! Subscribe to our MST Radio podcast to learn secrets of the trade.
ridodami4

Payne 394 upflow furnace

9 posts in this topic

HELP my air conditioner is out , when I start the unit I can hear the click for the motor but it doesnt start I need troubleshooting help Thanks the blower motor

Edited by ridodami4

Share this post


Link to post
Share on other sites

Need appliance parts? Call 877-803-7957 now!

Reach in there and turn the motor, does it turn free?. Check the capacitor for signs of swelling and leakage.

The relay might be clicking but not making contacts inside. A furnace uses low speed to operate the heat and is always wired to run on low. When air condition is called for the relay clicks and switches from low speed to high speed for cooling. Might be the contacts in there are fried.

Post some photos of your blower and the controls for a more precise answer. Let us see what you have if you can.

post-2707-0-07196600-1311891521_thumb.jp

Share this post


Link to post
Share on other sites

Thanks for the quick response, I love this site!

The motor spins freely and wht I think is the capacitor looks really ugly unit is about 20 yrs old and 2 years ago I replaced the circuit board as soon as the wife gets home I will post some photos

Edited by ridodami4

Share this post


Link to post
Share on other sites

Capacitor may look like this :

4x760%20run%20cap.jpg

Share this post


Link to post
Share on other sites

Here is a test to see if the motor is bad .

turn off power to unit

At the circiut board find and remove the PR-1 wire. move it out the way.

Find the black wire marked HI on the board . remove HI wire and place on PR-1 terminal.

You are now directly powering the fan motor(bypassing the circuit board) to test the motor .

Put cover back on blower and turn on power to heater. The motor will run now if it is ok.

If the motor runs replace the circuit board.

If the motor does not run replace the motor and capacitor.

Edited by ACtechGUY

Share this post


Link to post
Share on other sites

I ran the test ancd the motor runs, but not at full speed for air. Is the pic I posted the capacitor or the contactor and could this be the problem. if not capacitor where is it?

Share this post


Link to post
Share on other sites

If the motor runs by bypassing the control board , the problem is the control board . take loose the control board and look at the back of the board behind those small black boxes . you will likely see a burn mark. Regardless of wheather or not you see anything the board will have to be replaced .

It is often the case when a motor is failing it will draw alot more amperage than the relay contacts are rated for and burn out the board.

It is very possible to have a failed / failing motor and a burnt control board.

Share this post


Link to post
Share on other sites

SUCCESS!!!!! Replaced the capacitor, no luck . Pulled the blower motor and it was bad, replaced it today and the wife is smiling again!

Total cost $198.99. thank you all for your responses, Ridodami4