Jump to content
Click here to check out our structured, online appliance repair training courses for rookies and experienced techs.

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 30 March 2024 02:00 PM Until 03:00 PM
      0  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This workshop is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      If you have a specific appliance problem you'd like us to talk about, post it here! We need a problem statement and a PDF of the tech sheet or schematic so we can all see it on screen share. If you have a PDF that isn't already in the File library here at Appliantology, send it to us by attaching it to the contact form. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, March 30 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Trane XR90 light codes and problem


Bill Klika

Recommended Posts

Hello

Went to turn on our Trane XR90 unit today, and no luck with heat!

Unit is propane run, about 5 years old.

When I try to turn the unit on, it display a series of 3 flashes on the light indicator. The guide code says this is a "draft pressure error." Not sure what this means.

If I set the fan to "on", it blows air in the house, but not hot air.

I have absolutely no experience with this - do I call the repairman or is this something I can do?

Thanks

Link to comment
Share on other sites

  • Replies 8
  • Created
  • Last Reply

Top Posters In This Topic

  • Bill Klika

    4

  • jb8103

    2

  • RegUS_PatOff

    2

  • kdog

    1

... "draft pressure error."

does the Vent Motor run OK ?

Did any critters build a nest in your Vent system ?

Link to comment
Share on other sites

Sorry for the delay in getting back - snowstorm knocked out power until now!

Don't think there are any critters - will check vent motor. Can you provide any help on checking that? Is it as simple as turning fan to on?

Thanks

Link to comment
Share on other sites

AKA "inducer fan motor". Do a Google image search for "inducer fan motor" so you'll recognize it inside the furnace door. It draws combustion air from outside, through the combustion chamber where the burners are, then through the heat exchanger, then exhausting to outside typically through 3" PVC or 4" metal duct.

This fan motor (IFM) will come on first when the thermostat calls for heat. It will run for a while, usually 30 seconds or more, before the ignition cycle begins. There are pressure switches (at least one) which will detect the negative pressure caused by the IFM.

In your case a pressure switch is apparently not closing, but this can have a variety of reasons besides a faulty pressure switch.

When you remove the furnace door, very likely there is a door interlock switch which will de-energize the furnace when the door is opened. You can hold this switch closed, but be very careful if you do, because now the exposed wiring is live 120VAC. The IFM should be running when the furnace is running or when trying to start. If not, there is the problem. Touch the motor casing carefully, it may be very hot. Keep your hands away from wires.

If the IFM is happily whirring away, then you may have stopped-up condensate lines. Flexible tubing leads from the pressure switch(es) to a collection box and/or to the IFM casing. Flexible tubing drains the collection box and/or casing into a condensate trap or to a pump or directly into a drain in the floor. Disconnect those one-by-one and see if any water comes draining out. If so that's a problem.

Post pics if you get crossed up about any of this.

Link to comment
Share on other sites

Well, I tried several of the options - and indeed, we had hornets make a nest in the exhaust. It now works fine.

Thank you to everyone who had a suggestion!