Jump to content
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 27 April 2024 02:00 PM Until 03:00 PM
      5  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological. 
      We have a special session planned for this one. Instead of the usual Show 'n Tell on a technical topic, we're going to post tech sheets in the comments to this Calendar Event (scroll down to see what's posted so far) and ask specific questions that can only be answered by reading the tech sheet. If you at least try to answer the questions beforehand, you'll get a lot more out of it. 
      I'll be posting a couple more tech sheets before Saturday so be sure to follow this event to keep up with the tech sheets we'll be going through. 
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, April 27 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

YORK H2RC042S06B condenser unit


rolandvz71

Recommended Posts

OK I am by fair a A/C tech but I do understand voltage to a certain point.

 

Problem:

Outside contactor energizes and nothing is happening....evaporator fan is running inside but no cold air

 

Checked Compressor and it OHMs out good

Also checked the fan and it too checks out good!

 

Checked voltage @ the main panel 120v to GND (L1 and L2) and 240v across (L1 to L2)---good!

 

Now I followed this vid   

and here is what I get.....

 

w/the contactor energized (inside fan running) w/24V @ the coil --- voltage readings @ L1 & L2 @ the bottom of contactor 120v to GND but phase to phase I get 0v. @ the top of the energized contactor  I get 120v to ground, but phase to phase I get 0v. I should be getting 240v on top and bottom of a energized contactor.... right?? The only hmmm I hear is the contactor....no motor trying to start--- nothing!

 

So I think I have a problem w/my FLUKE meter....Soo I check the voltage @ the panel--- 120v to ground (L1 and L2) and 220v phase to phase (L1 to L2).

 

Now get this.....when I shutdown the system down OFF @ the thermostat the contactor DE-energizes I get 120v on one of the incoming lines and 0v on the other incoming line.....what the heck is up!?!

 

Is there something in the evaporator unit I am missing??

 

1st thing I thought it was was a bad capacitor just because it seemed to show all the signs of a bad cap ...its happened before so I took it upon myself to replace it and I still get nothing....

 

Its getting hotter in SE Texas need some guidance! 

 

Thx all~~!

Edited by rolandvz71
Link to comment
Share on other sites

What is the voltage reading inside the condenser disconnect panel?

Probably a bad disconnect breaker.

Link to comment
Share on other sites

It was the breaker outside that feeds the unit...getting 240V incoming and w/breaker closed getting 120V. Replaced breaker w/one from a big box store and she is now off and running! THX for  the good advice!

post-52397-0-29731700-1369168690_thumb.j

Edited by rolandvz71
  • Like 1
Link to comment
Share on other sites

By chance does anyone have a electrical drawing of this unit....the one outside is faded and one 1/2 is damaged from the heat......thx!

Link to comment
Share on other sites

I've been searching ...

do you have a part number of the diagrams ?

Link to comment
Share on other sites

I've been searching ...

do you have a part number of the diagrams ?

The only part # I see is the one I tittle of the post.....Am I not looking in the right spot on the condenser ?

Link to comment
Share on other sites

The only part # I see is the one I tittle of the post.....Am I not looking in the right spot on the condenser ?

 

do you have a part number of the diagrams ?

:rolleyes:

Link to comment
Share on other sites

  • 2 months later...

I've been searching ...

do you have a part number of the diagrams ?

Diagram is faded

Edited by rolandvz71
Link to comment
Share on other sites