Bryant A/C causing problem


schlager

Recommended Posts

We have an 8 year old Bryant air conditioner for the house it's 3 ton. When it comes on it makes a major power draw, the lights in the house really dim and then after several seconds the unit makes a sort of lurch and resumes working. It may do this once it may do it several times or it may not do it at all. It seems to mostly happen at night or at least it is mostly noticed at night.

Had a repairman out and he replaced the contact and added a hard start. The next night it was doing the same thing.

They are supposed to come look at it again tomorrow.

Is there anything I can look for? Anything I should make sure the repairman looks for? I'll bet $20 it won't do it while the repairman is around but I'm going to give it a workout.

thanks,

Link to comment
Share on other sites

  • Replies 3
  • Created
  • Last Reply

It may be a loose connecton in the main electrical panel or a weak breaker . perhaps you better let a qualified electrical contractor check your panel both the main and at the unit itself.

Link to comment
Share on other sites

  • 1 month later...

replace the start capacitor.

the lights dim so the compressor is sucking up the juice but can't get started. Could it be overgassed and can't start under the pressure? Add a hard start capacitor kit.

Link to comment
Share on other sites

low side pressure reading should be around 68 pounds per square inch PSI

Link to comment
Share on other sites