Jump to content
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 27 April 2024 02:00 PM Until 03:00 PM
      5  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological. 
      We have a special session planned for this one. Instead of the usual Show 'n Tell on a technical topic, we're going to post tech sheets in the comments to this Calendar Event (scroll down to see what's posted so far) and ask specific questions that can only be answered by reading the tech sheet. If you at least try to answer the questions beforehand, you'll get a lot more out of it. The tech sheet and the questions are posted in the comments section below.
      Your mission, if you should choose to accept it, is to check out the questions for each one and try to answer them ahead of time. Then come to the Dojo to see how well you did! 
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, April 27 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Fixing my AC Split syst.


rbravo46

Recommended Posts

My AC 3 ton split syst. is not cooling right. The low presure side is 70 psi. & high

presure side is 250 psi. with 88 F. ambient temp. The Compresor is consuming

8 A. instead 13 A. The return pipe on Compresor is swething & the Evaporator is

working just at 25% of his capacity.    I have replaced the Blower but still no change.

What could be causing this problem ?    Thank for any help,:huh:

 

 

Link to comment
Share on other sites

  • Replies 4
  • Created
  • Last Reply
  • 2 weeks later...

[user=10647]rbravo46[/user] wrote:

My AC 3 ton split syst. is not cooling right. The low presure side is 70 psi. & high

presure side is 250 psi. with 88 F. ambient temp. The Compresor is consuming

8 A. instead 13 A. The return pipe on Compresor is swething & the Evaporator is

working just at 25% of his capacity. I have replaced the Blower but still no change.

What could be causing this problem ? Thank for any help,:huh:

Reply: That's a lot of difference in current. Like it's not doing much work at all. Take the actual temperature of the return line at the condenser input with a service thermometer and compare it to the guages pressure/temp readings. The difference should be less than 10 degrees and five is prefereable. If not - add freon.

Link to comment
Share on other sites

why did you replace the blower? If you replaced the blower did you replace it with the same speed blower or opt for more speed?

 if you did you messed up

 