Jump to content
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 27 April 2024 02:00 PM Until 03:00 PM
      5  
      All Appliantology tech members are invited to join in this workshop on all things Appliantological. 
      We have a special session planned for this one. Instead of the usual Show 'n Tell on a technical topic, we're going to post tech sheets in the comments to this Calendar Event (scroll down to see what's posted so far) and ask specific questions that can only be answered by reading the tech sheet. If you at least try to answer the questions beforehand, you'll get a lot more out of it. The tech sheet and the questions are posted in the comments section below.
      Your mission, if you should choose to accept it, is to check out the questions for each one and try to answer them ahead of time. Then come to the Dojo to see how well you did! 
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, April 27 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

themostat power dead


Swenny

Recommended Posts

My furnace and air went dead. 

Started troubleshooting by checking voltages at the thermostat, none.  My transformer produces 17 volts but it's not getting to the thermostat.  I trace the wire from the 24v transformer out to what I think leads to the outside compressor unit.  There I find the 220 volt box and a 110 volt romex line into the compressor but I see no 24guage thermostat wire there.  The 220 fuse all check out.

So what happened to my 24 volt therm voltage.  I believe it's suppose to route from the 24v trans to the air compressor unit? then back up to the thermostat.

This is a 20year old GE furnace and air unit. Probably due to be replaced but I can't afford it just yet so I'm trying to milk a few more years from this equipment.  I replaced the fan limit switch last year.

Any help would be appreciated.

Swenny

Link to comment
Share on other sites

  • Replies 3
  • Created
  • Last Reply

To make it easier to explain tell me what color wires you have at the thermostat and what terminals are they connected to. Such as terminal 'r' is red, 'w' is white, 'g' is green, and 'y' is yellow (these would be typical) - I am guessing the romex line is not 110v because there is no need to run 220v and 110v to the condenser (outside unit)

Link to comment
Share on other sites

thanks for the reply.  I have a honeywell ct87b therm unit.  Wires are connected as follows.

Red---Rh

green--G

Blue--Y

White--W

 

Link to comment
Share on other sites

Problem solved.  It was the 24v transformer, primary side was open. replaced with generic type and now all ok.

I was confused at first because I mistakenly thought another 24v transformer in the furnace room was the culprit. It ran to the door bell, not the thermostat.  The problem one was located inside the furnace and hard to get at.  Once I traced the wires it became clear.

I could have figured this out sooner but I have no schematic of my unit.

Thanks for your help.

 

Swenny