Jump to content
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 10 May 2025 02:00 PM Until 03:00 PM
      1  
      All are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is available to everybody, including you! You don't have to be a member of Appliantology to join the fun.
      When: Saturday, May10 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to register. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it. 

Embraco EM3D60HLT refrigerator compressor


Recommended Posts

Posted

Hello.  Could someone please tell me which is the Common, Start, and Run on this particular compressor? Correct me if I'm wrong but I would say, the very top is the common, bottom left is start, and bottom right is the start?  I just want to be 100% sure, because many have told me this isn't always the case, that I would have to check this compressors manual first, but I looked it up and can't find a wiring diagram for this one.  Thanks all!

  • Replies 6
  • Created
  • Last Reply

Top Posters In This Topic

  • citizenX

    2

  • vee8power

    2

  • joshua_trees

    2

  • Budget Appliance Repair

    1

Top Posters In This Topic

Posted Images

Posted

Pretty much the standard configuration. 

download2.jpeg

Posted

On any split phase compressor, the start winding will read more ohms, and the run will read a lower value. I do this:

I take an ohms measurement across all 3 combinations of 2 pins; the pair with the most ohms between them is start and run; the other pin is then common. Once you determine which pin is common, the higher reading between it and another pin is start, the lower is run.

Let' say you measure 3, 4, and 7 ohms across the pins. The 7 ohms is reading excludes the common; it's the start and run windings in series(3+4=7). The start and run windings are connected at the common. Then 3 is run, and 4 is start.

@citizenXWhere's the relay in the above diagram? 

Posted
28 minutes ago, vee8power said:

 

@citizenXWhere's the relay in the above diagram? 

Dunno. Not my diagram, just one I found on the internet showing the windings. Probably some new direct wire environmental mandate designed to sell more compressors. 😜

Posted
9 minutes ago, citizenX said:

Dunno. Not my diagram,

I thought it was a portion of a schematic; I can't make sense of it.

12 minutes ago, citizenX said:

Probably some new direct wire environmental mandate designed to sell more compressors. 😜

I knew it was government! As drawn, it won't work.

Posted (edited)

I think just a unconventional symbol for the relay or PTC between start/run windings, (That's not the symbol for a run capacitor, is it?).

That's the general common compressor terminal setup but some are found turned upside down from this displayed layout.