Jump to content
LIMITED TIME OFFER: Get up to $100 off tuition for Master Samurai Tech courses through November 30th ×
Click here to check out our structured, online appliance repair training courses for rookies and experienced techs.

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 07 December 2024 03:00 PM Until 04:00 PM
      1  
      All Appliantology tech members are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This event is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, December 7 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Goodman GMPNO-80-4


laxdef69

Recommended Posts

Posted

Kind of a weird one...the vent blower (A made up word, I mean the pump that induces the draft in the PVC exhaust pipe) is strong enough to make the pressure switch close...I can clearly hear it...but occasionally the furnace won't light.

If I jumper it out, it lights immediately.

There doesn't appear to be any cracks in the vacuum tube from the blower to the switch, and the switch shows continuity when tested under vacuum....

Any other ideas?

Under advice from a contractor I know, I checked all the drain lines,and they are clear (still not clear why i checked the drain pan and exhaust stack lines, but whatever).

Should I just replace the pressure switch and be done with it?  Although I HATE the idea of just changing a part without understanding why it failed in the first place.

Thanks!

  • Replies 4
  • Created
  • Last Reply
Posted

It is possible to have bad contacts in the pressure switch, even though the switch pulls in and clicks. To test you will need a vaccum guage of some type or manometer to verify that there is the proper pressure (negative) at the swtich.

The switch is rated at -0.85"w.c. (water column is a measurement of low pressure- 28"w.c. = 1psi)

Switch part#  B13701-50

Posted

Thank you for the fast response!

I don't have a vacuum guage, I just sucked in a little bit on the vaccum hose and tested for continuity.

I'll replace the part and hope...thats again!

Posted

You checked the exhaust PVC flue because if it settles over time and the proper drain angle is not kept, the moisture will build up and cause the exhaust pressures to fall.  This in turn cause the pressure switch to change state.  There is a prescribed fall of X inches per Y feet of horizontal run.

Posted

Tons of slope in the flue pipe...so that's not an issue.

Thanks for the info though...always glad to add to the knowledge bank...

Changed the pressure switch, and all is good now!

Thanks again!