Jump to content
LIMITED TIME OFFER: Get up to $100 off tuition for Master Samurai Tech courses through November 30th ×
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 07 December 2024 03:00 PM Until 04:00 PM
      1  
      All Appliantology tech members are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This event is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, December 7 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Payne PG8MAA 042090ACJA gas furnace


nlodowski

Recommended Posts

Posted

I have a nearly new Payne PG8MAA 042090ACJA gas furnace that is giving me fits.

Background:

Furnace worked fine for about a month (once we sorted out some overheating, updraft issues) then the furnace fan was running but no heat.  I was getting alternating 13 and 31 codes and traced it to a connection problem.  Apparently as I was moving the old unit out of the basement, I knocked a sensor wire off its clip.  Found the wire off, clipped it on and things worked again. 

Soon after the furnace started tripping the breaker a few seconds after it was turned on and we were getting a constant quick flashing code.  (polarity) However nothing was changed as far as the 120v wires are concerned.

After resetting the breaker several times I was trying to get the furnace running and then POP goes the circuit board.  Had a service company take a look and told me the board was fried.  Ordered and installed a new board, I've also tightened the connections at the breaker and put a new switch in the line.  Now we are back to the fast flashing code and tripping the circuit breaker.  I'm afraid if I start playing with it again, I will fry another board.

Can anyone help?

  • Replies 1
  • Created
  • Last Reply
Posted

Number one rule of troubleshooting is never reset a breaker until you find the reason it tripped.

Perfect example was when I serviced Commercial Kitchen Equipment at an area hospital.

5 ton compressor for a big walk-in freezer tripped breaker. Another mechanic just reset it without finding why. BAM blew the main feeder to the hospital. Power company sent our boss a bill with a lot of big numbers. :P

Mechanic got two weeks off with no pay and I got chewed out for not watching him.:argue: