Jump to content
LIMITED TIME OFFER: Get up to $100 off tuition for Master Samurai Tech courses through November 30th ×
Click here to check out our structured, online appliance repair training courses for rookies and experienced techs.

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 07 December 2024 03:00 PM Until 04:00 PM
      1  
      All Appliantology tech members are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This event is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, December 7 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Air Conditioning Start-Up Checklist


Bobice

Recommended Posts

Posted

This convenient air conditioning start-up checklist has been designed to help maximize reliability, economy, and fuel conservation in the operation of air conditioning equipment.

Information from the files of the Hartford Steam Boiler Inspection and Insurance Co. indicates that a great many failures take place at start-up or early in the cooling season because of inoperative controls or safety devices. Most of these accidents could have been prevented if a little more attention had been paid to readying the equipment for service. It is therefore recommended that the following measures be taken to ensure a trouble-free cooling season and reduce the likelihood of equipment malfunction.

The tips offered here are intended to complement and not replace the recommendations of the equipment manufacturer.

COMPRESSORS

• Energize the crankcase heaters for at least eight hours before start-up and before taking insulation resistance readings of hermetic motor windings. Crankcase heaters should be left energized for the rest of the season so that whenever the compressor is idle, the heater will prevent refrigerant “migration” to the crankcase.

• Test the lubricating oil for color and acidity, and check crankcase oil level.

MOTORS

• Check the air passages of open motors for cleanliness and obstructions.

• Check the condition of and lubricate bearings.

• Take insulation resistance readings. If the readings indicate less than one megohm resistance, don’t start the motor. Check for the cause of the low resistance.

MOTOR CONTROLS

• Inspect starter contacts for deterioration from short cycling, arcing, or corrosion.

• Check terminal connections for tightness.

• Examine the overload protection for defects, and for proper size.

• Check mechanical linkages for binding and excessive looseness.

• Check timing devices for correct operating sequence.

OPERATING AND SAFETY CONTROLS

• Determine that the controls are properly calibrated and in working order particularly thermostatic controls, oil pressure safety switches, and flow switches.

REFRIGERANT CIRCUITS

• Be sure the circuit is equipped with a moisture indicator and if moisture is indicated, install new liquid line filter-drier cores. Determine and correct the source of the moisture.

• Check the expansion valve for proper operation and superheat settings over the full range of operation.

CONDENSERS AND EVAPORATORS

• Ensure that proper cleaning of heat transfer surfaces for the type of unit in use has been completed prior to operation.

• Cooling towers: Check the baffles for tightness and soundness. Clean the baffles, sump, and the spray nozzles. Check the make-up water valve for proper operation.

PUMPS

• Check the bearings, packings, shaft couplings, and seals. Lubricate bearings.

FANS

• Check for broken, cracked, bent, or loose blades. Check hubs, fan shaft, and bearings.

• Check the belt condition and belt tension.

• Replace air filters.

PIPING

• Check all piping supports for signs of distress.

• Check for external damage and excessive vibration.

 