Jump to content
LIMITED TIME OFFER: Get up to $100 off tuition for Master Samurai Tech courses through November 30th ×
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 07 December 2024 03:00 PM Until 04:00 PM
      1  
      All Appliantology tech members are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This event is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, December 7 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Question about American Standard compressor crankcase heater


crosstalk

Recommended Posts

Posted

The subject unit appears to have a 1.5 pole contactor (one leg switched and one leg passes through unswitched).  Based on my reading on this forum, this unswitched component is used to power part of the motor windings which function as a resistive compressor crankcase heater in this mode.

Should I be pulling the electrical disconnect (or turning off the breaker) during the winter to reduce power consumption?  Any reason to keep the crankcase heater powered all winter?  How much current is being drawn when idle?

  • Replies 2
  • Created
  • Last Reply
Posted

Yes there is reason to keep the crankcase heater energized. Its purpose is to prevent migration of liquid refrigerant to the sump of the compressor which can do damage to the compressor on start up.  Refrigerant will condense into a liquid in the coldest spot of the circuit and the lower pressure resulting from the condensation to liquid will cause more refrigerant vapor to take its place. This migration and condensation will continue until there is a pressure temperature equalization.  By artificially heating the compressor, you drive the liquid refrigerant out of that section of the circuit and reduce or eliminate the damage it causes on start up.

The crankcase heater is a purely resistive circuit so to calculate its power consumption use the power formula of W=IxE where W= Watts I= Amp draw that the heater is using E= the applied voltage.

A typical heater draws anywhere between 0.15 and 0.35 amps  (measure yours to know exactly what it is consuming at that time).  Assuming 230VAC applied supply voltage multiplied by the 0.15 to 0.35 amps gives you 34.5 - 80.5 Watts. 

If it is NOT a heat pump then you can shut down the condensor for the winter if you want to; however, there will come the warm days that you will need or want AC for short or limited times and the Manufacturers always recommend energizing the heaters 12-24 hours before starting the AC cycle to allow time for the liquid refrigerant to be boiled off and the oil to be warmed up.

I would personally not mess with it considering the minuscule cost of running the heater versus the cost of not and then damaging the compressor.  There are other ways to save pennies in electrical bills that do not have such costly consequences.  The choice is yours though - a few pennies per day for sound and solid insurance for your machine or risking a few thousand dollars out of pocket (as an unexpected expense) for a compressor or whole condensor change out due to broken crank, bent valves, or oil loss/failure damage that the heater is designed to reduce or eliminate.

If your compressor DOES NOT have an independent crankcase heater at all (belly band or bullet style in a well) and all you have is a single pole contactor - one contact and the other side barred - then it is incorrect to believe that the windings inside the compressor are energized at all times and heating the compressor.  Single phase motors (1 line of power in 1 line out) can be safely stopped by breaking only one line of power.  You can break both lines by using a two pole contactor; however, the minimum is one leg/line/pole.  The Manufacturers use single pole contactors as a production/money saving feature (they cost less per unit than installing a 2 pole - less cost = more profit to them and still does the job).  In this case, with no independent crank case heater, you gain/loose nothing by leaving the condensing unit on.  There is no current flow through the motor windings as you have broken the circuit ( if there was current flow you then would have an unintentional circuit and a defective/grounded winding(s)).  No current flow means no cost to you.

Posted

Thanks for the great information.  Maybe I misunderstood an earlier post on the function of the barred side of the contactor.