Jump to content
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 28 June 2025 02:00 PM Until 03:00 PM
      0  
      All are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is available to everybody, including you! You don't have to be a member of Appliantology to join the fun.
      When: Saturday, June 28 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to register. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it. 

Help...Indoor Blower won't shut off on this unit


atcherservice

Recommended Posts

atcherservice
Posted

I am working on a 15 year old Carrier Gas Pack unit that the Indoor fan blower runs even when the unit is not calling for cooling or heat. I have replaced the Iindoor fan relay, and still the same results, I am wondering if the Time Delay relay needs to be changed out. Have never come accross this situation any feed back would help.

Thanks

Ken

Atcher Service

[align=right]progress.gif[/align]

  • 4 weeks later...
  • Replies 2
  • Created
  • Last Reply
Posted

If you disconnect the thermostat does it still run all by its lonesome? How does the heat come on? Fan/limit? Maybe the limit is stuck?

  • 1 month later...
Posted

First check that there is not a high ohm short to ground in the blower motor that is causing it to find an alternate electrical path and making it run.

Second, if the unit has a Honeywell combination fan limit switch in the heater section and the unit is in a high ambient condition in some attic or closet, check to see if it has not changed state and energized the circuit

I had a church unit - only runs on Sunday - in a mechanical closet that the ambient air got hot enough for the bi-metal combination switch to spin and energize the fan circuit as if the heat exchanger had come on.  I adjusted the cut in temperature a bit higher - greater than the room temperature that could not be vented or conditioned - and this shut the fan circuit down.

Also, check to see if an open limit switch in the heat circuit is causing the fan to run.