Jump to content
LIMITED TIME OFFER: Get up to $100 off tuition for Master Samurai Tech courses through November 30th ×
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 07 December 2024 03:00 PM Until 04:00 PM
      1  
      All Appliantology tech members are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This event is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, December 7 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Lennox diplomat 80MGF blower works for heat but not a/c


jcoleman71

Recommended Posts

jcoleman71
Posted

I have a Lennox Diplomat 80 MGF, went to turn on the A/C today and the blower never kicked on. I switched it back to heat and it worked as normal. I had the blower motor replaced last fall so I doubt that would be the problem, I don't think it's the thermostat, it is just a simple thermostat and I put the red and green wires together and still no blower. I tried switching the fan lever from AUTO to ON and still nothing. The outside unit comes on just fine and I can feel the cold air coming into the HVAC unit but the blower never kicks on and it doesn't sound like it is even trying to come on. Do I look to replace the circuit board at this time or could it be something else?

  • Replies 2
  • Created
  • Last Reply
Posted

Check for 120V at the various calls for indoor blower by energizing "Y", "G", and "W" individually on the low voltage terminal strip.

Note that when "W’ is energized, the blower is delayed 45 seconds.

If there is 120V to each motor tap but the blower does not operate, replace the motor.

If there is not 120V at the Motor when "Y", "G", or "W" is energized, replace the control.

For service manuals and lots of other goodies,

become an Apprentice==> http://appliantology.org/apprentice/

Posted

On gas heat type furnaces the blower uses 2 speeds Red for low speed heat and black for high speed ac

Electric heat uses one speed wide open.

So a way to switch speeds from low speed fan for gas heat to hi speed fan for air conditioning is done by use of a fan relay.

Older units use a relay, newer units use pc boards. Just thought I would throw that in.