Jump to content
LIMITED TIME OFFER: Get up to $100 off tuition for Master Samurai Tech courses through November 30th ×
Click here to check out our structured, online appliance repair training courses for rookies and experienced techs.

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 07 December 2024 03:00 PM Until 04:00 PM
      0  
      All Appliantology tech members are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This event is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, December 7 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Lennox G20


lakshman

Recommended Posts

Posted

The fuse keeps blowing out when I turn on the AC. The furnace works well if I ask for heat. I looked for shorts and was not able to find any. I also investigated if there were shorts on the external unit - everything there is OK. What are my options?

Thanks,

-Luke

  • Replies 3
  • Created
  • Last Reply
Posted

Critter chewed the thermostat wires maybe, Weedeater got to the wires maybe.

Posted

Not really - those wires look clean and the terminals are connected. I do not see any issues at that end.

Posted

I agree with the weedeater or critter. here is how you check the wire going outside. You have a dead sgort(wire to wire) or a short to ground.

disconnect the 2 wire at the furnace and at the condenser leave them hanging in the air. Take an OHM reading between the 2 wires . you should get no resisatance of any kind . then check each wire to a good ground. again you should get nothing . Tie one end of the wires together. take a reading . it should be very low resistance (less than 10) .

If those check out then the problem is in the condenser most likely.

Check for resistance to ground on the wires going into the condenser control circuit . there should be none.