Jump to content
LIMITED TIME OFFER: Get up to $100 off tuition for Master Samurai Tech courses through November 30th ×
Click here to check out our structured, online appliance repair training courses for rookies and experienced techs.

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 07 December 2024 03:00 PM Until 04:00 PM
      0  
      All Appliantology tech members are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This event is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, December 7 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

AC just can't manage florida heat


LLAMBERT

Recommended Posts

Posted

Heres the digits. air temp before the coil 75, past the coil 65. R22 pressures low side 74, high side 210. Had the ducts replaced. Insulation added is next step. unit about ten years old any thoughts?

  • Replies 3
  • Created
  • Last Reply
Posted

75 PSI has it lugging.. With the house cool you oughta be around 68 PSI

Posted

thanks, I'll adjust it. house itself is 78-90 not cold enuf for swmbo.

Posted
75 PSI has it lugging.
SAY WHAT?? HUH?? What you talkin' ' bout Willis???
R22 pressures low side 74, high side 210
Suction pressure of 74# is normal for a 75 degree air temp . No problems there.

Head pressure of 210 is low if it was hot outside, and I can guess it was really hot outside like in the 90's.

Here are some general rules of thumb for R-22.

At 95 degrees outside you will see somewhere around 275 # head pressure. maybe just a bit lower for a higher efficicancy unit.

Suction pressure often mimics the entering air temperature . If you have 75 degrees entering air temp , your suction pressure will likely be somewhere near 75# psi. Weird but often true.

You need to confirm what type of metering device you have. If you have a piston or cap tube metering device , you may have a " Partial No Pump " compressor. The symptoms are low head pressure (in relation to the outside temp),along with a higher than expected suction pressure ( in relation to the inside temp)

If you have a TXV (thermostaic expansion valve) , you may be simply low on refrigerant. With txv's you can have a high suction pressure when you are low on charge. One indicator of low charge is low head pressure . I would expect to see higher pressure than 210 when it is very warm outside .