Jump to content
LIMITED TIME OFFER: Get up to $100 off tuition for Master Samurai Tech courses through November 30th ×
Click here to check out our structured, online appliance repair training courses for rookies and experienced techs.

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 07 December 2024 03:00 PM Until 04:00 PM
      1  
      All Appliantology tech members are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This event is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, December 7 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

comfortmaker C9MPD050F12A3 furnace control?


Recommended Posts

Posted

I have a comfortmaker C9MPD050F12A3 and the heat does not work. The a/c, fan and thermostat all work. There is a seperate furnace control and electronic gas valve. The gas valve has the diagnostic light and the limit switches and the exhaust blower hooked to it. The gas valve diagnostic light says all is fine but the is no power to the exhust blower and the pressure switch is open as called for. There are 6 wires from a block at the furnace control to the gas valve. I do not know what reading I should be getting on these lines to tell if it is a faulty furnace contrlol or gas valve. Anybody know how to test for this?

  • Replies 7
  • Created
  • Last Reply

Top Posters In This Topic

  • comfortless

    4

  • RegUS_PatOff

    3

  • applianceman18007260692

    1

Posted

At the Furnace there should be 24v AC between R and C.

When "heat" is selected, there should be 24v AC between W and C

Posted

The problem is not at the thermostat lines. I believe it is either the furnace control (an electronic board) or the gas valve (an electronic control device) and I wish to know how to test these devices.

Posted

do you have the 24v AC there where it should be at those times ?

Posted

All gas valves use solenoids. Each solenoid is rated diff. But each solenoid have one thing in common. They must have continuity.

Posted

If you have the 24v and there's no Error Codes

then it's sounds like a bad Controller

OR a bad Inducer Blower Motor

Heating (W) Request:

• 24 VAC signal applied to W terminal of FCB.

Inducer motor turns on and the pressure switch(es) close(s).

• Following a 15 second prepurge delay, after the pressure switches closes, the igniter begins a 17 second warm−up.

• The gas valve is energized, the main burners light and flame is sensed.

• The igniter is de−energized after the main burners ignite.

• FCB will delay blower operation for the 30 seconds timed from the opening of the gas valve.

Posted

Thanks I thought it might be a bad controller. There is no power going to the inducer motor.