FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 07 December 2024 03:00 PM Until 04:00 PM
      1  
      All Appliantology tech members are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This event is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, December 7 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Recommended Posts

Posted

I HAVE A GOODMAN FURNACE THAT IS BLINKING 5 TIMES ON THE LED..THE VENT FAN COMES ON AND THEN AFTER A FEW SECONDS THE BLOWER FAN STARTS AND THE LED BLINKS 5 TIMES OVER AND OVER...THE HIGH LIMIT CIRCUT IS CLOSED..TROUBLESHOOTING SAYS 5 BLINKS MEANS IT IS SENSING A FLAME AND THE CAUSE IS A STUCK GAS VALVE...I DONT THINK THAT THE GAS VALVE IS STUCK OPEN AS THERE IS NO FLAME OR GAS???I AM THINKING CHANGE THE CONTROL BOARD...ANY IDEAS.THANKS FOR ANY HELP

  • Replies 4
  • Created
  • Last Reply

Top Posters In This Topic

  • hawgwildtours

    3

  • jumptrout

    2

Top Posters In This Topic

Posted

Well if there is no flame the gas valve would be stuck closed.

On a call for heat use your volt meter to verify low voltage at the gas valve.

If you have voltage tap on the gas valve with the handle of a screwdriver.

This sometimes will open the valve.

If this works,replace the gas valve.

If it does not work,replace the gas valve not the control board.

If you do not have voltage at the gas valve,verify all circuits(roll out switches,pressure switches) etc. from the board to the valve.

Re-set,repair or replace the defective part.

Posted

It never gets to the stage to open the valve. It never sends power to the glow igniter

Posted (edited)

I am sorry. When you stated the high limit circuit is closed I mistook that as power to the ignitor.

Edited by jumptrout
Posted

It was the board. Replaced last nite. All is well. Thanks