Jump to content
Click here to check out our on-demand appliance repair training webinars.

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 04 January 2025 03:00 PM Until 04:00 PM
      0  
      All Appliantology tech members are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This event is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, January 4 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Soleus Air SG-DEH-45-1 Dehumidifier not removing humidity


Recommended Posts

Posted

I have a Soleus Air SG-DEH-45-1 Dehumidifier. It powers up and the fan runs but not getting any water in the bucket.

  • Replies 19
  • Created
  • Last Reply

Top Posters In This Topic

  • FDrozd

    9

  • kdog

    4

  • RegUS_PatOff

    4

  • Samurai Appliance Repair Man

    1

Posted

Compressor needs to run as well, will not run in dry or cold ambient conditions

Posted

The room is warm around 70 and humidity on the unit says 65. I lowered it and still same. How do you check the compressor? I felt the black cylinder shape item and it felt warm. Tubes leaving it were lukewarm

Posted

It needs to be humid in the room to trip the anticipator to start the unit - set control to a lower setting and see if compressor cuts in (should be audible) - try a boiling kettle in front of the unit so as to draw the steam into airflow. If the unit starts there is a good chance it is too dry.

Posted

The compressor does turn on. I have had it running about 30 min no humidity being removed. Compressor is not

Sorry Compressor is hot

Posted

I have a Soleus Air SG-DEH-45-1 Dehumidifier. The fan runs the compressor also comes on but no water being removed. Please help. Not sure what I need to look for or do. Seems like only the bottom front coil gets slightly cold with a little dampness

Posted

... Seems like only the bottom front coil gets slightly cold with a little dampness

the entire Coil should be evenly cold

else you may have a sealed system Freon leak

Posted

Grand Master Funk what would my next steps be in trying to repair this unit? What should I be looking for? Is this something that can be fixed?

Posted

if there's a system leak, it's usually not worth fixing ..

Posted

Thank you

Posted

Is there anything else that have these symptoms. I really don't see any oily residue anywhere.

Posted

If the Coils aren't evenly cooling, there could be a leak anywhere.

Slow leaks usually don't leak oil.

Posted

Topics Merged

Relative humidity needs to be high to cause these to sweat the coils - to test frost pattern, disable the fan and run compressor only - see how the coils frosts

Posted

Disconnected fan and compressor ran hot and no coils freezing

Posted
:boohoo:Sealed System repair
Posted

Is this something I can tackle as an above average tinker person

Posted

Is this something I can tackle as an above average tinker person

Service Equipment

Listed below is some of the equipment needed for proper servicing of refrigeration systems.

• Evacuation pump - Robinair, Model 15600 2 stage, 6 cubic feet per minute pump is recommended.

• Four-way manifold gauge set, with low loss hoses

• Leak detector

• Charging cylinder

• Line piercing saddle valve - (Schroeder valves).

• Swagging tools

• Flaring tools

• Tubing cutter

• Flux

• Sil-Fos

• Silver solder

• Oil for swagging and flaring Use only part # R0157532

• Copper tubing Use only part # R0174075 and # R0174076

• Dry nitrogen 99.5% minimum purity, with -40°F or lower dew point

• Crimp tool

• Tube bender

• Micron vacuum gauge

• Process tube adaptor kit

• Heat trap paste

• ICI appliance grade HFC134a

  • Team Samurai
Posted

Electrolux makes a very nice training DVD on this if you're seriously wanting to do this ==> http://www.repaircli...4454883/1192226

gallery_4_4_36076.jpg

Posted

Never have worked on one. Wonder what the low side pressure should be. Anybody know?

Posted

(Schroeder valves)

i think that is the peanuts kid who plays Beefoven on the piano...