Jump to content
LIMITED TIME OFFER: Get up to $100 off tuition for Master Samurai Tech courses through November 30th ×
Click here to check out our structured, online appliance repair training courses for rookies and experienced techs.

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 07 December 2024 03:00 PM Until 04:00 PM
      0  
      All Appliantology tech members are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This event is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, December 7 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Recommended Posts

kcamp99186
Posted

Hi. This is Ken Campbell and I'm new to the forum.

I have a Goodman Furnace GMPN080-4 that is blowing the 3A fuse on the control board. The issue is the AC won't work. I replaced the fuse only to have it blow when power was reapplied. Thermostat calls for cooling but I have nothing. AC and furnace breakers are ok. Furnace fuse is good too. I can manually operate the contactor on the condenser and confirm that it is working. Can anyone point me in the right direction please?

  • Replies 7
  • Created
  • Last Reply

Top Posters In This Topic

  • kcamp99186

    3

  • Hiroshi

    2

  • leamy

    2

  • alamo1718

    1

Posted

contactor winding may be shorted. common issue .. ants, moisture, Chinese crap design....

try disconnecting the 24 volt connector on contactor and see if fuse pops

 

Leamy

Posted

So by "confirm that it is working" means both the compressor and condenser fan motor kick on when you "manually" operate the contactor? For the contactor to work correctly it needs to be able to close itself...

1) A demand for cooling is initiated. · The control checks for an open limit. If an open limit is detected the furnace will remain inoperable until the condition is corrected. During an open limit condition the circulating air blower will be energized. The status light will blink four (4) times. ·

2) The condenser contactor will close. ·

3) After approximately five (5) seconds the circulating air blower will start on the cooling speed. ·

4) After the room thermostat is satisfied the condenser contactor will open. · The circulating air blower will remain in operation for approximately sixty (60) seconds.

If you are blowing fuses at step 2, what Leamy says makes sense- because that 24v circuit has to pull the contacts together before anything receives power...and you have been testing it "manually," I am guessing that means you are pushing the contacts together yourself?

kcamp99186
Posted

Yes, I do mean pushing the contactor closed by hand and the fuse blows immediately when power is switched back on. I replaced the fuse with a 5A, all I had left, just to see if it would blow and the AC ran fine.

I believe the thermostat wire is bad. I had spliced it several years ago where it wore against the frame. While it was running again, I decided to check it and the compressor shut down as I moved the wire about. Wiggling the wire caused it to start back up again.

I've shut it down and am replacing the thermostat wire today as well as the power wire from the outdoor shut-off. It has some damage as well. Does it sound like I'm on the right track?

Thanks for the help.

 

Posted

It sounds like a broken/shorting low voltage wire. When you install the new stat wire, feed it through some clear plastic tubing to protect it, before you install it.  You could even get real fancy and use some blue PVC conduit, ENT, from lowes or home depot. The ENT has ends that will screw into the control box and really protect the low voltage wire. I've even seen the wire sheath that you see in cars added after the wire its installed.   Don't forget to replace that 5 with a 3 amp fuse. It is sized to protect the transformer and other components. If it shorts again with the 5A still installed, it could take out something else. 

Posted

did the same thing a few years back came back to a open low voltage transformer and a finally totally smoked contactor.

check the contactor, or you may be back with more parts...

kcamp99186
Posted

Thanks so much guys. I found that the stat wire was rubbed bare inside the case. Must have been from vibration over the years. Replaced both the thermostat wire and the electrical cable. Put the electric in liquidtight conduit. Didn't think about the Thermostat wire. Will redo that soon! Good idea. And have replaced that fuse as well.

Appreciate the advice.

 